Joined
Nov 18, 2017
Messages
47
Reaction score
28
Location
Bridgend, South Wales
Afternoon All,

Maybe an odd question. For the last 8 years I've been in this industry I have always fitted single and 3 phase disboard/CU's with locks and no remote isolator other than on a locked main panel.

I'm on a new job where we are using a mix of Siemens 3 phase boards and Crabtree single phase boards, all of which have a sticker inside them.

"TO COMPLY WITH BS7671 All consumer units that are intended to be locked after installation must be supplied via a separate means of isolation fitted adjacent to the unit"

Anyone able to shed any light on this? Is it correct? What regulation states this?

A lot of these boards will be accessible to students. You can only imagine the havoc students would cause with a fully accessible isolator. o_O

[ElectriciansForums.net] Remote Isolator On Locked Disboard/CU
 
This looks like the beginning of another great myth which will soon be turning up on EICRs everywhere.

You can almost see the future on this one, hundreds of DBs with cheap isolators retrofitted to them with dodgy crimp connections to extend the feeds and contacts burning out all over the shop.
 
Only thing I can find is this: but it's stating that the isolator should be locked away..

[ElectriciansForums.net] Remote Isolator On Locked Disboard/CU
 
Emergency Switching, 537.4.2.5View attachment 45854

"Where a danger could occur" is far too vague for my liking. I could understand workshops or boiler houses where maintenance might be occurring, not accommodation.

Your talking about a location where every single phase final circuit is RCBO protected. Would an isolator really help any situation?
 
Dangers come in a variety of known and as yet unkown forms.
Presumably it's written vaguely to cover any current or future eventuallity.
RCBO protection may not be on all circuits in all installations.

For example in Student accomodation,
A Brown (or Black or Grey) cable hanging out of a light fitting in a corridor with the end of the cable showing copper.
Does that present a Danger?
 
Last edited:
Dangers come in a variety of known and as yet unkown forms.
Presumably it's written vaguely to cover any current or future eventuallity.
RCBO protection may not be on all circuits in all installations.

For example in Student accomodation,
A Brown (or Black or Grey) cable hanging out of a light fitting in a corridor with the end of the cable showing copper.
Does that present a Danger?


Brown, black and grey cables are all line colours so should be treated as such unless marked otherwise.

Having previously had a nasty belt from neutral to earth I'd also argue a blue cable would present a danger.

I still don't see how an external isolator would help?

What happens in more public areas where boards are locked in cupboards? Do we start fitting emergency stops everywhere with contactors on the supply to the board?
 
Dangers come in a variety of known and as yet unkown forms.
Presumably it's written vaguely to cover any current or future eventuallity.
RCBO protection may not be on all circuits in all installations.

For example in Student accomodation,
A Brown (or Black or Grey) cable hanging out of a light fitting in a corridor with the end of the cable showing copper.
Does that present a Danger?

Yes that presents a danger, or should at least be assumed to present a danger until proved otherwise.
But what is your point? Are you saying that there should be an accessible isolator adjacent to a locked DB in case this situation occurs?
 
It seems fair enough to identify the CU isolator as an emergency device. For example a room contains smoke and a smell of burning with no obvious source. What's the first-line response?
 
It seems fair enough to identify the CU isolator as an emergency device. For example a room contains smoke and a smell of burning with no obvious source. What's the first-line response?

So what happens in public buildings where boards are fitted in locked risers and store rooms? Do we put emergency stops in? Rotary isolators outside the doors?
 
It seems fair enough to identify the CU isolator as an emergency device. For example a room contains smoke and a smell of burning with no obvious source. What's the first-line response?
Activate the fire alarm and get out?
 

Reply to Remote Isolator On Locked Disboard/CU in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top