Ground floor lighting trips out mcb | Page 3 | on ElectriciansForums
Guest viewing is limited

Discuss Ground floor lighting trips out mcb in the UK Electrical Forum area at ElectriciansForums.net

Biggy

-
Joined
Dec 27, 2018
Messages
25
Reaction score
20
Location
Halifax
Hi everyone,

My first post but straight in with a couple of issues.

I'll start with a 6amp MCB that keeps tripping out relating to ground floor lights.
For your info:

There is 10 x 3w led recessed lights in Kitchen, 8 x 3w led recessed lights ,plus a main central Led light (approx 100watt equivalent ) in the room next to the kitchen and then the same amount of lights and Main central light in the Back room. I would say the combined wattage including two outside lights (40watt each) will be around 480w so let's call it 500watt on the ground floor.

From my understanding a 60w bulb draws around 0.5amp so in effect 30 of the 60w bulbs (around 1800watt combined ) would require a 15amp breaker which would be comfortable, so based on this theory is the 6amp MCB actually overload on 500watts on Ground floor and this tripping the breaker .

The breaker does not trip immediately as can take 5-10mins sometimes longer, and in some instances it has tripped even when ground floor lights have been OFF.

The joist spaces have all been insulated with rockwool if this makes any difference as I want to eliminate any possibility before I start questioning my electrician who advises that maybe I should fit a 15amp breaker in as he feels 6amp is less power for 30 odd lights .

Can anyone shed LIGHT on this :)

I'll come to the second issue after I can get a solution to this.

Sorry for the lengthy explanation but I know there's nothing more frustrating than not arming knowledgeable people will full info and expecting solutions. Hope I've not missed anything out.

Hope to get a few responses and guidance as I have basic understanding of electrics.

Thanks
 
Without knowing your competency and experience working with electrics, I would advise NOT to take the cover off the CU to swap cables onto a spare breaker.
Safe isolation or not, this is a job for a qualified spark.

That said, you don’t need a spare mcb... just swap the downstairs circuit with maybe upstairs lights circuit and see if the fault moves over too. Then you’ll know if it’s the wiring or a weak breaker. (Swap the neutrals over too, if they’re on different rcds)

Are you certain the breaker trips even with all switches off? This would rule out any lamp or driver.
Is there anything in the circuit that has a permanent supply from this circuit that isn’t a light? Someone has already suggested an outside PIR. What about doorbell transformer, smoke alarms, burglar alarm, electronic switches such as dimmers?
 
There is smoke alarms hard wired to each floor and a heat alarm in kitchen. On the same floor there is one smoke alarm and one heat alarm in different places.

They seem to operate fine by looks of it.
Did have a problem with them where they kept chirping but guy said it was a loose connector and pushed it in real tight and chirping stopped.

Nothing else powered by circuit I don't think other than lights .
Outside light bulb fitted now and linked to the circuit but nothing tripped just yet and I've left everything switched off now and come back home so will see if it flips down again in the morning, which it more likely will.
 
Looking at the photo, it wont be easy to swap the 2 circuits as you'll need to untangle the neutrals to swap them over as they will be on different neutral bars.
As I said before, its not advisable to go poking about in there if you're not experienced.
 
I think the only thing you could do yourself is check the wiring at the switches to see if any cables are damaged or loose . ( you may have already done this )
ensure the power is off when you do this .
you have a short somewhere and it may be a cable thats damaged by a screw cutting the insulation, possibly at a light switch.
it could also be damage by a nail or screw through a cable if you have had other work done.
If you are not competent with electricity I wouldn't advise opening the consumer unit.
despite you switching the power off , via the mains switch at the unit you can still be in danger of touching live cables/contacts and slight chance or arcing . also if you cross neutrals you will give yourself more heartache.
 
OK thanks for your input all, I have asked the sparky to come back and sort it out. He said he will pop round tomorrow so will see what he has to say about it.

I've not checked switches for loose connections but I'll get him to rectify all issues hopefully.
I'll update tomorrow sometime .

Thanks again.
 
Sounds like a lot of electronic power regulators involved here,
Any circuit with lots of electronics involved can have problems,
SMPS are highly reactive and cheap one's even more so !
So we don't know what harmonics are involved,
But they can increase the current flowing.
I would measure the current in the circuit.
If the cables will allow it change your breaker from 6 amps to 10 amps.
See if that helps.
 
No dimmer switches, just simple basic switches.

As for changing from 6amp to higher ampage I have been advised on this thread not to as 6amp should be sufficient to power up 1380watts and my combined wattage is not even 500watts so why increase the ampage ?
 
Unless it is certified that all the lighting circuit wiring is in 1.5mm^2 then the maximum 10A MCB is allowed. The 6A MCB should be more than adequate. If there are heavy switch-on current surges then a C6 (instead of a B6) MCB is allowed - that allows a higher short-term surge current before tripping. In your two photos, the cooker MCB seems badly out of alignment in the detailed close-up photo. That suggest that it was not fitted correctly or its mounting is damaged and it should be inspected by a qualified electrician.
 

Reply to Ground floor lighting trips out mcb in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
733
I fitted a Mem MR30 Pod and MCB, about £75 for both.
Replies
8
Views
2K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top