Hi Chaps,
This may be something simple but I'm not sure I understand it correctly.

Regarding spurs...

"The total number of Fused spurs is unlimited but the number of non Fused spurs should not exceed the total number of socket-outlets and items of stationary equipment connected directly in the circuit"

So I understand that say for example, on a ring, there are 4 double sockets, you can only spur once off of each socket of it is unfused.
The confusing part for me "the total number of Fused spurs is unlimited"
Does this mean that out of the hypothetical four double sockets on the the ring, you could pick one double socket, add a Fused spur, then have another Fused spur from that one, and then another Fused spur from that one etc etc etc
Or does it mean that from one socket outlet, you can add multiple fused fused spurs (providing that you could get all the wires in safely)

Thanks as always .
 
[ElectriciansForums.net] Clarification on the Regs...
appendix 15.
 
"the total number of Fused spurs is unlimited"

As is the number of points on the rfc is unlimited... so if each point on the ring can have a spur off....

In practice, you would never have 4 spurs off your hypothetical 4 double sockets on your ring.
 
I did look at it but was a bit baffled can understand it much more now.
Just needed some simpler wording for me to get my head around it!
Reading through the book religiously in an attempt to get a grasp, and keep a grasp of it all.
This forum is an absolute god send .
Thanks .
If you start at the top of the ring, and go anti-clockwise, the first thing you come to is a spur taken direct from the ring.
No socket, no FCU.
As you can see, you aren’t restricted to only taking spurs from sockets, it’s just easier.
You don’t have to use an FCU, though using one means you can have more than one socket on the spur.
 
As is the number of points on the rfc is unlimited... so if each point on the ring can have a spur off....

In practice, you would never have 4 spurs off your hypothetical 4 double sockets on your ring.
Not entirely true, you may have a RFC with NO sockets at all and only fused spurs, such as one feeding kitchen appliances
 
Hi Chaps,
This may be something simple but I'm not sure I understand it correctly.

Regarding spurs...

"The total number of Fused spurs is unlimited but the number of non Fused spurs should not exceed the total number of socket-outlets and items of stationary equipment connected directly in the circuit"

So I understand that say for example, on a ring, there are 4 double sockets, you can only spur once off of each socket of it is unfused.
The confusing part for me "the total number of Fused spurs is unlimited"
Does this mean that out of the hypothetical four double sockets on the the ring, you could pick one double socket, add a Fused spur, then have another Fused spur from that one, and then another Fused spur from that one etc etc etc
Or does it mean that from one socket outlet, you can add multiple fused fused spurs (providing that you could get all the wires in safely)

Thanks as always .
Take a good look at Appendix 15 , it gives you pictorial and written examples of what and how to connect to a Ring Final Circuit (RFC) you can spur off by means of a Junction box if you wish, a Spur is not limited by being connected to an existing socket outlet which forms part ot the RFC.
The Regulation covering this (sorry I only have the 17th edition it may be different in the 18th) is 433.1.204.
A spur cant also be use to supply an item of fixed equipment providing can meet the requirements of the stated Regulation ie a recommendation that equipment at 2 KW and above is given it's own dedicated circuit, things to avoid are Immersion heaters, Space heating etc.
I believe someone else has mentioned App 15, it's not really that hard to understand and the diagram goes a long way to help in the understanding.
Hope this helps.
Edit, with the inclusion of AFDs we may eventually see the demise of RFCs in favour of Radial circuits, protected by either, 20 A or 32 A OCPDs using 2.5mm2 and 4mm2 cable for 20A and 32A respectively.
 

Reply to Clarification on the Regs... in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

K
  • Question
Ah, I see. The op question is ambiguous, and I took it that he wanted to add a socket for a washing machine from and exiting switch fused spur. A...
Replies
10
Views
796
  • Question
Thanks for the advice.
Replies
11
Views
1K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top