Wiring RF thermostat receivers to valiant boilers...

We have been using standard 0.75mm 5 Core flex, from the receiver to the boiler (reference method B). Obviously the flex is carrying L-N-E at 230v and also two switch wires ‘boiler on’ ‘boiler off’ at 24v. However someone has made a comment on carrying band 1 and band 2 in the same cable, saying it’s not allowed. All conductors are insulated to 230v and the regs are like blurred lines.

Can anyone offer any advice?

Thanks
 
Wiring RF thermostat receivers to valiant boilers...

We have been using standard 0.75mm 5 Core flex, from the receiver to the boiler (reference method B). Obviously the flex is carrying L-N-E at 230v and also two switch wires ‘boiler on’ ‘boiler off’ at 24v. However someone has made a comment on carrying band 1 and band 2 in the same cable, saying it’s not allowed. All conductors are insulated to 230v and the regs are like blurred lines.

Can anyone offer any advice?

Thanks

Your setup complies with reg 528.1 (ii), so it is allowed.
As above, Induced voltage may be a problem.

[ElectriciansForums.net] Multicore cable voltages
 
No issues as long as the insulation of the conductors is rated at or greater than the maximum voltage it will be used with.

Induced voltage shouldn't be an issue here, as the 24V can be seen as a digital signal, either on or off. This depends on the impedance of the input to switch the boiler. Does it trigger a relay or is it to an input on a circuit board?
 
No issues as long as the insulation of the conductors is rated at or greater than the maximum voltage it will be used with.

Induced voltage shouldn't be an issue here, as the 24V can be seen as a digital signal, either on or off. This depends on the impedance of the input to switch the boiler. Does it trigger a relay or is it to an input on a circuit board?
The connection is a 24v RT terminal on the boiler circuit board. The Switching is done within the receiver.
 

Reply to Multicore cable voltages in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

The point is that you set up a schedule of what temperature you want at what time and the nest brings the heating on at the right time to achieve...
Replies
9
Views
2K
davesparks
D
  • Question
You need a wi fi switch that is compatible with your switchbot thermostats. Remove the SCR, use the neutral and live to power the wifi switch, and...
Replies
8
Views
727
  • Question
Dump of 26 to aid discussions
    • Like
    • Winner
    • Agree
Replies
10
Views
2K
  • Sticky
Hi Richard, thanks for your comment. The relay is rated 12A peak. It's also worth noting that a relay contact will perform differently depending...
    • Like
    • Winner
Replies
4
Views
2K
  • Question
From a technical perspective moving tbe pump is tbe simplest option which leaves you with the least number of potential failures.
2
Replies
32
Views
4K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks