I had a problem a couple of days ago with my boiler shutting down due to too high temperature difference between the input and output, which transpired to be because the boiler had been wrongly wired.

I have two zones in my heating system, so as I understand it there should be 5 wires between the controller and the boiler - L, N & E plus two switched live. But there was only a 4-core cable so the boiler had been wired in a slightly different way to accommodate this. Interesting to speculate whether the cable would have been fitted by the plumbing or electrical contractor in a new-build house! Anyway, it is what it is - but practically impossible to rectify as the two ends are on different floors and not directly one above the other.

The gas engineer who came to check it out rewired in a different way but acknowledged that it's still not optimal. He speculated that I may be able to do something with a wireless connection between the boiler and controller. Any ideas about how to do that, and what I would need to buy?

Thanks
 
On balance the wireless link is probably the neatest option. Moving the pump takes it from a cupboard to a usable store room so is marginally less suitable, though technically sound. But at least I have two viable solutions.

The system is already run through Hive. But moving that upstairs puts it one floor further from the router so anyway would not seem like a good idea, though it seems that doesn't work anyway - the issue is the power to the pump.
Thanks
 
On balance the wireless link is probably the neatest option. Moving the pump takes it from a cupboard to a usable store room so is marginally less suitable, though technically sound. But at least I have two viable solutions.

The system is already run through Hive. But moving that upstairs puts it one floor further from the router so anyway would not seem like a good idea, though it seems that doesn't work anyway - the issue is the power to the pump.
Thanks

From a technical perspective moving tbe pump is tbe simplest option which leaves you with the least number of potential failures.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Baku, Azerbaijan
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Enthusiast (Unqualified Hobbyist etc)

Thread Information

Title
Cable missing in central heating wiring
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
32
Unsolved
--

Advert

Thread statistics

Created
naylorpd,
Last reply from
davesparks,
Replies
32
Views
4,067

Advert

Back
Top