Hey all.

Im new to this forum. Seeing how limited d web is to rectifying any electrical queiries, i thought i might find this useful.

I am a warranted electrical domestic licencee. (Based on IET) and possess a Higher Diploma in Electrical Engineering. I live in Malta (EU) which uses a UK electrical based infrastructure. (TT system).

Just yeaterday as i was looking into a fault at a client, i realised something very strange regarding current draw. I plugged a 0.9KW hairdryer (3.9A @ 230v) into wall socket outlet and clamped live and neutral seperately. L read 4.2A and N read 3.6A. Unless my clampmeter requires calibration what is the reason of this variation???

The worst part is that when i clamped the hot conductor at the consumer unit main DP MCB, it marked that it was drawing 9.2A!!! (Yes, I have deducted the current that was being drawn from the house at that time). That is more than double what it should be marking. I understand that the cables from socket outlet to consumer unit might carry some extra resistance hence draw more current, but surely not to that extent!!!

Can anyone explain this other discrepancy???
 
Re #1: You might want to re-consider what you wrote:

I understand that the cables from socket outlet to consumer unit might carry some extra resistance hence draw more current, but surely not to that extent!!!

What is the accuracy of your ampclamp?

[ElectriciansForums.net] Current draw discrepancy
 
Hey all.

Im new to this forum. Seeing how limited d web is to rectifying any electrical queiries, i thought i might find this useful.

I am a warranted electrical domestic licencee. (Based on IET) and possess a Higher Diploma in Electrical Engineering. I live in Malta (EU) which uses a UK electrical based infrastructure. (TT system).

Just yeaterday as i was looking into a fault at a client, i realised something very strange regarding current draw. I plugged a 0.9KW hairdryer (3.9A @ 230v) into wall socket outlet and clamped live and neutral seperately. L read 4.2A and N read 3.6A. Unless my clampmeter requires calibration what is the reason of this variation???

The worst part is that when i clamped the hot conductor at the consumer unit main DP MCB, it marked that it was drawing 9.2A!!! (Yes, I have deducted the current that was being drawn from the house at that time). That is more than double what it should be marking. I understand that the cables from socket outlet to consumer unit might carry some extra resistance hence draw more current, but surely not to that extent!!!

Can anyone explain this other discrepancy???
Something else plugged in on that circuit? how did you measure the L and N of the Hair drier?
 
The live and neutral current must be equal, so clearly the meter was giving incorrect indications.Either it is faulty, or it cannot handle the current waveform that the hairdryer produces. Some hairdryers half-wave rectify the current to the heating element on low setting, i.e. although the supply is AC the current drawn is pulsating DC. This can cause an AC-only meter to read incorrectly and inconsistently. Even without the overall half-wave rectification, the waveform can be noisy and distorted due to the DC fan motor which also has a rectifier.

You cannot add or subtract currents from the rest of the installation to calculate the expected total reading at the consumer unit, unless they are all in-phase. If there is significant waveform distortion in the hairdryer current, then it will not add algebraically to the current from a true resistive load, for example. Therefore your expected total current may have been in error.
 
Thanks for your replies. However i still find myself confused.

Maybe i need to clarify..

The current reading at the consumer unit which is directly connected to the kwh meter is the actual current draw. The consumer pays depending on the current draw at the kwh meter.

In this case, with the hair dryer turned off, the kwh meter read 2.1A. With the clampmeter left in same place, when i turned the hairdryer on it read 11.3A.(which means that the hairdryer was actually drawing 9.2A!! I.e the consumer will pay on the 9.2A and not on the 3.9A rating of device). When clamped at the socket outlet directly where the hairdryer was connected, it read an average of 3.9A which makes sense according to its rating (900W at 230v.). My question is where is this massive current discrepancy coming from?

(Maybe i need to scrap my clampmeter??)

Thanks again
 
Hi - I don't know what's really going on, but I suspect it's a combination of your meter and how you are using it. For interest you could make up an extension cord and test some loads. Type of load, position of clamp and proximity to other fields may all affect the reading.
 
Please clarify (-even more :) )the it I have highlighted in bold - is it the kWh meter or your ampclamp (or the hairdryer).

In this case, with the hair dryer turned off, the kwh meter read 2.1A. With the clampmeter left in same place, when i turned the hairdryer on it read 11.3A.

and later:

When clamped at the socket outlet directly where the hairdryer was connected, it read an average of 3.9A which makes sense according to its rating (900W at 230v.).
 
Last edited:

Reply to Current draw discrepancy in the UK Electrical Forum area at ElectriciansForums.net

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top