Kinross
This is supplying a small commercial set up. SWA is only 16mm and the isolator is rated at 100A. Earth cable between MET and SWA is only 10mm.
How would you code it? Having a brain fart and thought I'd seek other opinions.
[ElectriciansForums.net] Thoughts on this set up
Poor workmanship certainly the Swa needs proper protection KMF 60 amp
2Core not ideal the armouring, when terminated correctly, may be sufficient for CPC, but not for Main Bonding Protective Conductor😎
I’d say there’s been a proper set up before… with the gland into a box.. seeing that there’s a shroud there.
Also old screw holes in the back board suggested there’s been old equipment removed…. Like an older style meter.
Agree on C2 for unsheathed cables…. It may be in a lockable enclosure ( hopefully it’s got a door and is lockable!) but it’s available to untrained personnel to open up and read the meter.
The unsheathed cables are definitely a C2.
The lack of overcurrent and fault protection is a C2 as well.
The G/Y cable may be OK. It depends on what the earthing system is in the commercial unit.
Reply to Thoughts on this set up in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
    • Friendly
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...