I just wanted to make sure I understood the new regulation above.

I am about to replace some ELV downlights with mains voltage, do these now have to be 30mA RCD protected?

At present they have 100mA protection and the earthing is TT.

Cheers.
 
This is going to create quite a bit more work on some occasions then isn't it!
There is a spare way on the 30mA side but then that means putting the lights on the same side as the sockets.
It's a starbreaker board and there seems to be so many different configurations of the RCD's that I'm bound to get the wrong one if i choose to replace the 100mA RCD! They all have different holes in different places. (should have opened the CU up!)
I think it's the same one as last time, i.e the one you gave me Tel, but not sure.
[ElectriciansForums.net] Understanding 411.3.4, RCD's for lights.
 
Actually after a quick scan of the net..
Is this the right one to replace the 363/S100
https://www.NoLinkingToThis/p/crabtree-starbreaker-63a-30ma-dp-type-ac-rccb/29042
 
I haven’t the latest addition, but under the previous, guidance from my Scheme, when replacing luminaries (like for like) in a bathroom for example, there was no requirement to ensure of addition protection.

The installation of additional luminaries would.

What does the new reg state?
 
IMO that would be the installation of new circuits, or the alteration of existing ones. I’ve been wrong before, guess one would need to ask a grown up.
I've been asked to move the security light motion detector "round the corner of the building". It's all surface mounted cables and the associated light is not moving. I'm thinking an upgrade to RCD isn't mandatory, but very happy to be shown the error of my ways.
BTW - there is an earth at the fitting :) .
 
I've been asked to move the security light motion detector "round the corner of the building". It's all surface mounted cables and the associated light is not moving. I'm thinking an upgrade to RCD isn't mandatory, but very happy to be shown the error of my ways.
BTW - there is an earth at the fitting :) .
Assuming this is domestic then you have two choices because the circuit has been altered/extended.
1. Put in place additional rcd protection.
2. Carry out a risk assessment which must prove that omitting additional rcd protection is not detrimental to the safety of the installation as your works are a departure from BS7671.
 

Reply to Understanding 411.3.4, RCD's for lights. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
Replies
17
Views
528
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
445
davesparks
D
  • Question
Good point, I was assuming an up-front RCD is for fault protection within DB, etc, and to cover for a failed RCBO for fault conditions, not as...
Replies
6
Views
2K
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
1K
  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
627

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks