Wondering if anyone can advise as I’m struggling to understand the regs, I’ve never tested or even worked on a TT system.
I have tested an old farm that has been converted to a school so it is no longer an agricultural premises.
The main supply is a three phase PME which feeds all 6 consumer units. However 2 of the consumer units have been converted to TT off the same rod. The earth from the SWA has been left disconnected in the three phase panel so the PME has not been exported.
The SWA feeds one consumer unit with a front end 30mA RCD, which this consumer unit then feeds another consumer unit off in an old barn (now being used for storage) with another 30mA front end RCD. Obviously we have selectivity issues with this setup but that’s not my main concern.
The main issue is that this sub-main is just being fed from a 40A MCB in the three phase panel.
Would I be correct in saying I need a 100mA S type RCD to protect the sub-main?
My plan is to install a separate plastic enclosure next to the three phase panel which will house a 100mA S type RCD, using double insulated tails from the panel to the RCD which will then have the SWA on the outgoing to feed the 2x consumer units on the TT.
I will also replace both front end RCD consumer units with double pole RCBOs for all circuits (except the circuit that feeds the second consumer info to avoid selectivity issues).
Is my understanding correct?
I have tested an old farm that has been converted to a school so it is no longer an agricultural premises.
The main supply is a three phase PME which feeds all 6 consumer units. However 2 of the consumer units have been converted to TT off the same rod. The earth from the SWA has been left disconnected in the three phase panel so the PME has not been exported.
The SWA feeds one consumer unit with a front end 30mA RCD, which this consumer unit then feeds another consumer unit off in an old barn (now being used for storage) with another 30mA front end RCD. Obviously we have selectivity issues with this setup but that’s not my main concern.
The main issue is that this sub-main is just being fed from a 40A MCB in the three phase panel.
Would I be correct in saying I need a 100mA S type RCD to protect the sub-main?
My plan is to install a separate plastic enclosure next to the three phase panel which will house a 100mA S type RCD, using double insulated tails from the panel to the RCD which will then have the SWA on the outgoing to feed the 2x consumer units on the TT.
I will also replace both front end RCD consumer units with double pole RCBOs for all circuits (except the circuit that feeds the second consumer info to avoid selectivity issues).
Is my understanding correct?