ZEDEZ

-
Joined
Aug 10, 2015
Messages
76
Reaction score
51
Location
London
I installed a kitchen ring recently. Went back to test after the builders had finished and found that the CPC is broken somewhere inaccessible, everything else tests normal. I’ve got continuity on live conductors, and even with the broken CPC, each socket is connected to the CPC and tests with an acceptable Zs value.

What are my options to be able to sign this off without any destructive investigation / remedial work?

My first thought was to split the ring into two 20a radial circuits. But it would be preferable to leave it connected as a ring for increased capacity.

As far as I understand it the fact that the CPC doesn’t have ring continuity isn’t affecting safety or disconnection times, so is there a reason I couldn’t sign this off and simply note this fact?
 
It would be nice if the OP joined in regarding the broken CPC, is there any junction boxes on this ring or is it completely all new? From experience when a cable has been screwed it has caught one of the other conductors. The OP needs to find exactly where the break is first ( a cable come out hopefully will be the cause) and what loads are likely to be on each leg.
 
I had this twice before where the same kitchen fitter on two different jobs drilled straight through a t&e and unbelievably took out the cpc and neutral first time and just cpc broken second time

First thing I used to do was mark out cupboard positions and where we'd be chasing cables in , followed by getting the fitter to ok it.....

First time this prat got away with it
as customer wouldn't let us take a cupboard down even though we showed him all cables disconnected and continuity on one leg and lack of continuity, position of chase and cupboard screws, fitter had altered the layout and not thought about his fixings etc

Fitter thought it was funny and laughed it off saying it was our fault and we should do a better job

Managed to replace cable with a jb above a cupboard and fished cable down capping to socket

Second time I got the long lead and went round the suspect area testing to all the cupboard screws got continuity to 2 screws ,
Customer was a pita awkward type who always gets what they want

but I was actually quite glad of this in the end because he went mad insisting Kitchen cupboards were removed so we could sort it out

Fitter went AWOL wouldn't answer his phone but this guy tracked him down and somehow got him to agree to footing the bill for our rework , repairing the ceiling and making good the chases and decorating plus he had to fit cupboards again
 
I installed a kitchen ring recently. Went back to test after the builders had finished and found that the CPC is broken somewhere inaccessible, everything else tests normal. I’ve got continuity on live conductors, and even with the broken CPC, each socket is connected to the CPC and tests with an acceptable Zs value.

What are my options to be able to sign this off without any destructive investigation / remedial work?

My first thought was to split the ring into two 20a radial circuits. But it would be preferable to leave it connected as a ring for increased capacity.

As far as I understand it the fact that the CPC doesn’t have ring continuity isn’t affecting safety or disconnection times, so is there a reason I couldn’t sign this off and simply note this fact?
I would say further investigation needed, I would be surprised if its anything other than earthwire clamped to green sleeving remove cables and check, sorted
 
No i agree. Im not debating its wrong at all. But for my own interest....say a eicr. Comparing it to the situation i just gave. Electrically is it unsafe??

It's unsafe in the sense that you know for a fact a cable has been physically damaged somewhere, and so needs repairing or replacing.
 
It's unsafe in the sense that you know for a fact a cable has been physically damaged somewhere, and so needs repairing or replacing.
A conductor that in a healthy circuit isnt carrying current and in the event of a fault for 0.4 seconds. Im not by any means promoting broken rings. I get the end to end on line conductors for current carrying capacity. But as i stated before 4mm 32amp. 1.5mm cpc.
 
A conductor that in a healthy circuit isnt carrying current and in the event of a fault for 0.4 seconds. Im not by any means promoting broken rings. I get the end to end on line conductors for current carrying capacity. But as i stated before 4mm 32amp. 1.5mm cpc.

I see your point, but you can't issue a satisfactory certificate because it doesn't pass testing.
 
If it's a damaged cable not sure how the cpc is cut and not at least one of the live conductors. Unless it's a loose connection in an inaccessible j/b?

I had a similar fault when carrying out a first visit and found no cpc to some of the sockets. Dug the photos out for you. Some investigation and cutting the back of a kitchen cupboard out revealed a huge lump of silicon and a bunch of holes. Clearly done before the cabinets were put in. Once I had pulled off the silicon you could see the blown apart cable they tried to cover up. By all accounts the kitchen was fitting 4 years ago, metal sockets everywhere and all signed off. Customer wasn’t impressed.
[ElectriciansForums.net] Question regarding signing off 32a ring circuit with broken CPC ring continuity


[ElectriciansForums.net] Question regarding signing off 32a ring circuit with broken CPC ring continuity
 
4mm circuit 32amp ocpd has a 1.5mm cpc. Why is it different?? I was questioning this the other day. Obviously readings compliant to operate in required time.

Hi - I agree, a radial of 2.5/1.5 cable with B32 OLCP will clear a fault without damage, provided max Zs is met.

Overload is wrong of course :) . And in this case the cable may have other damage than the assumed clean break in the cpc.
 

Reply to Question regarding signing off 32a ring circuit with broken CPC ring continuity in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
5K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top