Fusing of fans to comply with manufacturers recommended instructions | Page 2 | on ElectriciansForums

Discuss Fusing of fans to comply with manufacturers recommended instructions in the UK Electrical Forum area at ElectriciansForums.net

Joined
Sep 9, 2013
Messages
12
Reaction score
2
Location
irvine
Manufacturers want there fans fused to 3a on the permanent feed but the switch wire is still on the 6a MCB doing an eicr is a c2 if there is no RCD protection
 
Hi - sorry to be a party pooper, but a BS1363 3A fuse is more sensitive to overload than a BS60898 6A mcb. For example, the 3A fuse will always melt at 6A but the mcb will never trip.

[ElectriciansForums.net] Fusing of fans to comply with manufacturers recommended instructions
 
Manufacturers instructions are usually nonsensical, inappropriate and unattainable; a bit like the serving suggestions on food packaging



Might be nonsensical but as per The Wiring Regulations which in the UK we have to follow the manufacturers instructions supersede the Regulations and the greatest knowledge of all the electrician
 
Might be nonsensical but as per The Wiring Regulations which in the UK we have to follow the manufacturers instructions supersede the Regulations and the greatest knowledge of all the electrician

This is not the case. The regulations ask us to "take account of" manufacturer's instructions. This has recently been changed from the previous wording of "must be followed"

The reason for this is the proliferation of less than useful or appropriate info that is included in some products. Some would ask us to install to lesser standards than BS7671 asks.
 
Might be nonsensical but as per The Wiring Regulations which in the UK we have to follow the manufacturers instructions supersede the Regulations and the greatest knowledge of all the electrician

Rubbish. Manufacturers instructions are for guidance only and yes we have to take account of them. But we do not have to follow them, especially when they are wrong.

In this case,
1. FCUs are not needed or used on lighting circuits which are already adequately protected.
2. A 3a FCU offers no discrimination against a 6a MCB in spite of 'Contacts' post above.
3. The fuse is to protect the cable, not the device on the end of it. It would be non compliant for a manufacturer to fit a cable so small it required 3a protection.
4. How would the manufacturers instructions be complied with in all the other countries where FCUs are neither available nor compliant?
 

Reply to Fusing of fans to comply with manufacturers recommended instructions in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...
Replies
2
Views
667
Yes, it would give some measure of user protection but probably not in the case of a fire.
Replies
23
Views
2K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top