Fusing of fans to comply with manufacturers recommended instructions | Page 3 | on ElectriciansForums
Discuss Fusing of fans to comply with manufacturers recommended instructions in the UK Electrical Forum area at ElectriciansForums.net
irvine
Manufacturers want there fans fused to 3a on the permanent feed but the switch wire is still on the 6a MCB doing an eicr is a c2 if there is no RCD protection
Hi - Out of curiosity I have asked manufacturers what this is all about but they've been tight lipped. I have seen fans that don't spec 3A fuses and they seem to have a fuse on the control board and/or claim they've a thermal overload for the motor.
[ElectriciansForums.net] Fusing of fans to comply with manufacturers recommended instructions
I’m not sure. Shall I ask Winston1 on diynot.com? He keeps banging on about exactly this, in the same way that you do.
He also has a thing about transformers, and not having 13A sockets on lighting circuits too.
Exactly the same bees that you have in your bonnet. Hmm, makes you wonder, do you have a long-lost identical twin?
Reply to Fusing of fans to comply with manufacturers recommended instructions in the UK Electrical Forum area at ElectriciansForums.net
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...
Yes, it would give some measure of user protection but probably not in the case of a fire.