Fusing of fans to comply with manufacturers recommended instructions | Page 2 | on ElectriciansForums

Discuss Fusing of fans to comply with manufacturers recommended instructions in the UK Electrical Forum area at ElectriciansForums.net

Joined
Sep 9, 2013
Messages
12
Reaction score
2
Location
irvine
Manufacturers want there fans fused to 3a on the permanent feed but the switch wire is still on the 6a MCB doing an eicr is a c2 if there is no RCD protection
 
Hi - Out of curiosity I have asked manufacturers what this is all about but they've been tight lipped. I have seen fans that don't spec 3A fuses and they seem to have a fuse on the control board and/or claim they've a thermal overload for the motor.

[ElectriciansForums.net] Fusing of fans to comply with manufacturers recommended instructions
 
I’m not sure. Shall I ask Winston1 on diynot.com? He keeps banging on about exactly this, in the same way that you do.

He also has a thing about transformers, and not having 13A sockets on lighting circuits too.

Exactly the same bees that you have in your bonnet. Hmm, makes you wonder, do you have a long-lost identical twin?
 
Why not just wire the bathroom with a 3 amp fuse to the lighting and fan then wire everything downstream off the fused spur, problem solved

Shouldnt be a sfcu doing the whole bathroom as the ideal of a local isolator is to isolate the fan itself without interrupting other supplies ie.. lights.
I always put a 3a module fuse holder in a click mini 3 apparatus faceplate along side the 3pole isolator. On 1st fix i always mark the loop in loop out cable and they get paired into the top of fuseholder, thus making perm live & sw live 3A protected.

Do i think its OTT. Yes!
Do i do it to cover my own ---. Yes!
Will the fan manufacturer be able to point liability at me if the fan goes up in flames . No!!
 

Reply to Fusing of fans to comply with manufacturers recommended instructions in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
even allowing for diversity this sounds a bit tight for a 100 amp supply, can you tell us what the existing circuits actually have connected to...
Replies
2
Views
626
Yes, it would give some measure of user protection but probably not in the case of a fire.
Replies
23
Views
2K
Definitely, although most likely within the accessories. I've often found that once accessories are disconnected the cabling IR is fine. Sometimes...
Replies
19
Views
2K
  • Question
I received the latest Guidance Note 4 - Protection Against Fire yesterday. My first observation is it's the first guidance note I've ever known...
2
Replies
43
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks