How to actually TT a shed/garage? | on ElectriciansForums

Discuss How to actually TT a shed/garage? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Supporter
Joined
Dec 18, 2011
Messages
5,278
Reaction score
5,773
Location
Gloucestershire
I have never TT'd a shed/garage I always just extend the earth from the house.

In the example of a shed/garage being supplied with SWA is the armour of the SWA earthed by the house (lets say TNCS) or by the earth rod?

Also, if the SWA is earthed by the TNCS then you have both TNCS and TT present in the garage CU. If the SWA is earthed by the TT then you have TNCS and TT present in the Main CU? Is that ok with regards potential difference between earthing systems?

ps... I realise you can extend the equipotential zone but I am just looking at a TT for a shed, this is because of the chance of an electric charging point being in the shed (as per my other thread).
 
Last edited:
Earth the armour at supply then gland in to a plastic box to isolate the earth.

Connect shed CU to Rod.
In your example there will be a plastic adaptable box near the shed. From this box there will be (for example) 10mm Twin and earth in to the garage CU. Will this earth be connected to the TNCS or TT? You will have the same issue with the TNCS and TT being in the same box/CU, is this a problem?
 
can't see any reason not to use the TNC-S and add a rod at the shed.
the argument for not using TNC-S is the problem caused if the supply neutral is lost. adding a rod would solve that problem. tin hat time .
[ElectriciansForums.net] How to actually TT a shed/garage?
 
Wasn’t that their intention for the 18th until they redacted it because North of the border they can’t sink rods in granite. Same issue but a shed.
 
At the end of the day you'll never eradicate all risk. PME has some potentially severe flaws but these are very rare.

The biggest of these being in contact with true earth and losing the supply neutral.

IMO whatever you do will always have a potential downside.
 
In your example there will be a plastic adaptable box near the shed. From this box there will be (for example) 10mm Twin and earth in to the garage CU. Will this earth be connected to the TNCS or TT? You will have the same issue with the TNCS and TT being in the same box/CU, is this a problem?
Gland the supply cable off within an all insulated enclosure. Take no other cpc into it, earth the consumer unit to the electrode.
 
Gland the supply cable off within an all insulated enclosure. Take no other cpc into it, earth the consumer unit to the electrode.
Do you mean use a 2 core cable from insulated enclosure to garage CU? Maybe just have the insulated enclosure very close to the garage CU and just continue the 2 core of the SWA into it, perhaps directly behind it. That way you only have the 2 cores (without an earth) for a very short distance?
 
I'm going to extend the example now!!

If the shed/garage is going to have sockets/lights AND an electric vehicle charging point would you need to take 2 separate supplies (i.e 2 x 2 core SWA) as the charging point needs to be on it's own dedicated circuit? Or could it be on it's own dedicated circuit from the Garage CU? I would have thought the former as otherwise it's not really a dedicated circuit.
 
I wouldn't dick around with two supplies, split the tails at source, switched fuse then supply to the shed/garage in a suitable installation method and suitable DB. TT if required for the EVCP or other services or PME if acceptable.
 
If the cable going to shed is sufficient with installation method and size for the sockets, lights and thr charger then you can supply it from the house cu. Then the shed/garage cu has seperate circuits for each of the 3 above. I would where possible have the rcd protection in the shed rather than house in this instance.
 
Wasn’t that their intention for the 18th until they redacted it because North of the border they can’t sink rods in granite. Same issue but a shed.
Most of Donegal's rock but it's a requirement there to have an Earth electrode in every installation. Can be hard work sometimes.
 
Regarding the question of terminating the SWA and ensuring you can't simultaneously touch exposed-conductive parts from two different earthing systems, I use a 25mm nylon compression gland on the shed/garage DB for the SWA rather than an SWA gland. After R1+R2 tests, I cut the armour off using the standard method, and leave the serving sheath the same length. I make sure the compression gland insert is completely on the sheath when tightened, but with not much inside. The end of the armour is enclosed within the body of the compression gland, out of the reach of fingers (from inside the board), meeting IP2x requirements. It's a lot neater than using a separate insulating box, containing a "proper" SWA gland.
 
You can purchase plastic glands for SWA to isolate the earthed armour from the shed.
Do you have a link? When I search for plastic swa gland I just get stuffing glands.
 
I see no reason not to use a stuffing gland as long as the cable is properly secured by cleats etc.
A bit of heat shrink over the end of the cut end of the armour will keep it neat, just remember not to shrink it until after the Zs test
 
I'm going to extend the example now!!

If the shed/garage is going to have sockets/lights AND an electric vehicle charging point would you need to take 2 separate supplies (i.e 2 x 2 core SWA) as the charging point needs to be on it's own dedicated circuit? Or could it be on it's own dedicated circuit from the Garage CU? I would have thought the former as otherwise it's not really a dedicated circuit.

Apologies if this has been covered but If supplying a ev point I think youll need something like 40a (min depending on size of charging point) with no diversity allowed? (not done the course but im sure thats right) so in a normal house you'd probably split the tails into a new small board purely for the ev. Based on that if you were powering a shed that subsequently supplied an ev you might have to take that into account? If just a shed then its unlikely youll be using that much power at one time but might be worth considering??
 

Reply to How to actually TT a shed/garage? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
587
  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
628
  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
608
  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K
  • Question
I think the original was 'no lyrics'
2
Replies
25
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks