There is a thermal overload shown in the schematic. How come this is not fitted?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Siemens RCCB trips even while inductive motor is off in the Talk Electrician area at ElectriciansForums.net
It is used for all kinds of materials, steam sterilizer. Clothing, cleaning, etc. Materials for a cleanroom.Nicelectrician: What is/will the autoclave used for please?
The situation is that the RCCB actually trips.The same transformer that provides the supply to the 'Power fail' relay has another secondary coil which provides the 24V ac for the various electrically operated solenoid valves(V1 etcetera). The load of one or more of these valves being energised could be loading the transformer such that the voltage to the 'Power fail' relay has a temporary dip, opening it's contacts briefly, and then recovering to close the contacts - yet the PLC detects the brief opening of the contacts and assumes a 'Power Fail' has happened.
Check the output voltages of the secondary coils and also any marking for the voltage rating of the primary coil - is the primary suited to 208V or is it a 220V/230V/240V primary?
I dont have much tools to test, The only option to "test" that I have is to change it. I m already planning to do so. But if you know a method to troubleshoot the RCCB I m all ears.Have you carried out any tests on the RCCB in case that is at fault?