Hi guys, sorry I haven't really send all the details about this, I've attached a photo of the diagram that the manual says, It says to put thermal overload relay? plus fuse upstream the soft starter? I'll be using this for a pump, I've also attached the photo of the details of the pump. Thanks much for helping and responding!

[ElectriciansForums.net] Do I need over current protection?

[ElectriciansForums.net] Do I need over current protection?
 
There is a common misconception in the UK that overloads need setting at more than the FLC, but normally they should be set at FLC as they are designed so that they cope with the inrush fir that setting.

It's a hangover from the old oil filled dashpots that were used for OL protection. These you had to have set at 100% FLC.

In regard to the OP, if the manufacturers state you need OL protection, then you need it. Maybe this model of SS doesn't have built in OL protection.
 
Fuse it (or use MCB) upstream of the starter to protect the equipment from short circuit, and use the overload to protect the motor from overload. You can use a combination MCCB for the complete protection provided it is of the correct type and is adjustable to the nominal motor current.

In the UK our regulations state that all motors above 0.37kW must have overload protection, I imagine your regulations will be similar.
 
Fuse it (or use MCB) upstream of the starter to protect the equipment from short circuit, and use the overload to protect the motor from overload. You can use a combination MCCB for the complete protection provided it is of the correct type and is adjustable to the nominal motor current.

In the UK our regulations state that all motors above 0.37kW must have overload protection, I imagine your regulations will be similar.
Yes, but, remember BS7671 is irrelevant when it comes to machiney.
110.2,xi
 

Reply to Do I need over current protection? in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
801
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
833

Similar threads

Also use a tails gland and clamp if available and make sure tails are secured to a wall. The danger here is a live to earth fault in the Consumer Unit
Replies
7
Views
569
Well at about 9.30 last night I stripped the door card off and found the culprit, cable snapped and end off. So I spent another hour and managed...
    • Like
    • Funny
Replies
2
Views
289

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top