Is the consumer unit fed by a cut-out ? Or a sub main ?Hi everyone I'm ready to do second fix on a rewire it's a tt system all my circuit will protected by individual rcbos
Do I need main switch to be normal dp switch or time delay rcd please help.
Then as said if all circuits are rcbos and the Ra is low enough then a main switch is fine.Mains 100amp fuse
Thank youif every circuit is protected by individual RCBOs then a main double switch is fine
Big respect thanksThen as said if all circuits are rcbos and the Ra is low enough then a main switch is fine.