Was adding an RCD to a consumer unit so that both sides are protected, basically I’ve took the 2 lives from the load side of the main switch to the tops of the Rcds, then there’s a neutral going from the load side of the main switch to the first neutral bar I’ve doubled up a neutral there and took it to the top of the new (one closest to main switch) rcd. Then out other end I’ve took a neutral to the first neutral bar. Also from the first neutral bar I’ve took one to the top of the 2nd Rcd and then out the other side I’ve took it to the 2nd neutral bar. I’m getting 230v between live and neutral right through the new rcd but it won’t trip when I press the test button and also isn’t tripping when I’m doing RCD test on it. Am I doing something daft when connecting that up??
 
[ElectriciansForums.net] Adding RCD to existing Consumer Unit

that how its done, example .
 
Last edited:
Are the neutrals on both sides of the 1st RCD connected to the same neutral bar? They shouldn't be.
Short answer - do what you have done with the live from the main switch with the neutrals, and each RCD has its own neutral bar on the load side.
For each RCD, the load neutrals need to be independent for it to see an imbalance.
 
I would have that right hand side busbar fitted properly.

As for adapting an existing CU... cant you take the guts out a new dual rcd board and make it fit? You would have the right number of neutral bars, the right neutral links made up to the right length etc
 

Reply to Adding RCD to existing Consumer Unit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
833
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
931

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top