Hi everyone,

I have read few posts about dual appliance outlet and wonder now if it can be used in my case. I have 32a 6mm cable to 45a switch supplying 6200w hob. Current oven is 2,4kw 13a plug. It will be replaced with 7,4kw induction hob and 3,6kw oven. Can hob circuit be used for both appliances connected to dual outlet plate and using same 45a switch? We were told by an electrician 6mm cable will be ok for both appliances, but when we had a quote for new kitchen they builder told us he would not connect both appliances to one 6mm cable and we heed to add new circuit. In our case it has to run outside around house and we would like to avoid it if possible.

Any advice is appreciated
 
Why are you listening to a builder where electricity is involved.

What you propose sounds fine to me all being as it sounds.
Good point, if I was not told by electrician first I would believe builder, but he supposed to discuss the issue with his electrician. I don’t know what his electrician said, but we have extra cost £325 for new circuit and 85 for rcbo. Our house built 2000 and we are rcd protected, of course I don’t want extra cost if possible.
 
Now your answers made me wonder, what else I was told wrong by the builder. When we had kitchen ceiling insulated an electrician had to extend some cables including 6mm hob circuit. My spouse got involved in the conversation with electrician and he got confused thinking we wanted move the hob to opposite side. We decided not to remove the cable, in case we want to move hob or oven to opposite side. Please see how it ended up, if I remember correctly. Again builder said, that electrician was wrong to do it, as line to another side should not come out from junction box, but after 45a switch. Where circuit must have two module enclosure with two circuit breakers, one for hob, one for oven. Now I also wonder if it is so necessary to do or it can be left the way it is now.
 

Attachments

  • [ElectriciansForums.net] DUAL APPLIANCE OUTLET PLATE
    image.jpg
    369 KB · Views: 31
builder should stick to slopping bricks.. 6mm on a 32A into a 45A isolator is good fot cooking appliances upto a rating of 15kW. end of.
15!!? When I said, we wanted 11kW for both appliances and were told by electrician it would be ok, our precious builder said, that appliances can not be installed, as cable will be running on it limits and can over hit. After his words I lost interest talking to him. But two month later he send us his quote with lots of possible extras. After it, I said buy kitchen in Wickes and left over spend in pub. I guess last me for long with current lockdown.
 
what you have to bear in mind is diversity. with cooking appliances yo won't usually have all elements on at the same time, and they cycle on annd off with the thermostats, so a cooker /hob rated at say 11kW total rated power ( 48A) will have an average current of only approx. half of that (24A).
 
what you have to bear in mind is diversity. with cooking appliances yo won't usually have all elements on at the same time, and they cycle on annd off with the thermostats, so a cooker /hob rated at say 11kW total rated power ( 48A) will have an average current of only approx. half of that (24A).
11kW was total 7,4 hob and 3,6 oven and it what I said to the builder that that both appliances will not be run on full, but he said it would be dangerous and illegal. I want everything to be done according regs in case I have to sell or rent house in the future.
 
not to worry. as i said, both oven and hob will be fine on a 32A MCB, 6.0mm cable (if cable is not smothered in insulation) . this application of diversity has been in use for 60+ years and found to be compliant. only reason to install separate circuits for oven and hob would be to isolate either if faulty and still have use of the other.
 
but he said it would be dangerous and illegal.
As previously stated, let him worry about slopping bricks together and let the electrician deal with the electrics. TBH if a builder that I had employed started coming out with comments like that he would be looking for business elsewhere.
 
the only illegal thing here is a builder sticking his snout into something about which he knows bugger all (and probably due a nice backhander from his tame sparks odd job man to install an uneccessary circuit).
 
not to worry. as i said, both oven and hob will be fine on a 32A MCB, 6.0mm cable (if cable is not smothered in insulation) . this application of diversity has been in use for 60+ years and found to be compliant. only reason to install separate circuits for oven and hob would be to isolate either if faulty and still have use of the other.
(if cable is not smothered in insulation) - we have vaulted ceilings so cables runs between roof and 100mm celotex and in the walls between terminal bricks and plasterboards without conduits. Roof can get hot in the summer, but there is a air gap between roof and celotex to prevent condensation.
 
cables warm up in use. this is normal. as long as the heat can dissipate, there's no problem. covering cables in insulation reduces their current capacity, the derating factor dependent on how thick the insulation over the cables is.e.g. 6mm cable with no insulation is rated at 47A continuous. derating due to insulation can be as much as 40%. a reasonable air gap around the cable is recommended where cable is heavily loaded.
 
cables warm up in use. this is normal. as long as the heat can dissipate, there's no problem. covering cables in insulation reduces their current capacity, the derating factor dependent on how thick the insulation over the cables is.e.g. 6mm cable with no insulation is rated at 47A continuous. derating due to insulation can be as much as 40%. a reasonable air gap around the cable is recommended where cable is heavily loaded.
Because of vaulted ceilings our cable runs in air gaps between insulation and roof, I don’t know building regs for air gap in roof but I believe it minimum 50mm or more. Maybe it is not same as no insulation, but there is good air gap.
 

Reply to DUAL APPLIANCE OUTLET PLATE in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
582
  • Question
Great idea, thank you mate :)
2
Replies
38
Views
5K
  • Question
If your using 35mm or 50mm use 2 core SWA and use the armour as the earth, it'll cut down on price. I know people will comment on this but the...
Replies
10
Views
921
  • Question
I prefer to use the 5 core cable method, joining the two neutrals and two lives at the wall end. The connection blocks in these cookers seem to...
Replies
5
Views
2K
allowing for diversity a 32 amp supply will be fine for them both, but remember, the cable needs to be adequate to cope with a load on up to that...
Replies
4
Views
786

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks