Hi everyone,

I have read few posts about dual appliance outlet and wonder now if it can be used in my case. I have 32a 6mm cable to 45a switch supplying 6200w hob. Current oven is 2,4kw 13a plug. It will be replaced with 7,4kw induction hob and 3,6kw oven. Can hob circuit be used for both appliances connected to dual outlet plate and using same 45a switch? We were told by an electrician 6mm cable will be ok for both appliances, but when we had a quote for new kitchen they builder told us he would not connect both appliances to one 6mm cable and we heed to add new circuit. In our case it has to run outside around house and we would like to avoid it if possible.

Any advice is appreciated
 
what you have to bear in mind is diversity. with cooking appliances yo won't usually have all elements on at the same time, and they cycle on annd off with the thermostats, so a cooker /hob rated at say 11kW total rated power ( 48A) will have an average current of only approx. half of that (24A).
 
what you have to bear in mind is diversity. with cooking appliances yo won't usually have all elements on at the same time, and they cycle on annd off with the thermostats, so a cooker /hob rated at say 11kW total rated power ( 48A) will have an average current of only approx. half of that (24A).
11kW was total 7,4 hob and 3,6 oven and it what I said to the builder that that both appliances will not be run on full, but he said it would be dangerous and illegal. I want everything to be done according regs in case I have to sell or rent house in the future.
 
not to worry. as i said, both oven and hob will be fine on a 32A MCB, 6.0mm cable (if cable is not smothered in insulation) . this application of diversity has been in use for 60+ years and found to be compliant. only reason to install separate circuits for oven and hob would be to isolate either if faulty and still have use of the other.
 
but he said it would be dangerous and illegal.
As previously stated, let him worry about slopping bricks together and let the electrician deal with the electrics. TBH if a builder that I had employed started coming out with comments like that he would be looking for business elsewhere.
 
the only illegal thing here is a builder sticking his snout into something about which he knows bugger all (and probably due a nice backhander from his tame sparks odd job man to install an uneccessary circuit).
 
not to worry. as i said, both oven and hob will be fine on a 32A MCB, 6.0mm cable (if cable is not smothered in insulation) . this application of diversity has been in use for 60+ years and found to be compliant. only reason to install separate circuits for oven and hob would be to isolate either if faulty and still have use of the other.
(if cable is not smothered in insulation) - we have vaulted ceilings so cables runs between roof and 100mm celotex and in the walls between terminal bricks and plasterboards without conduits. Roof can get hot in the summer, but there is a air gap between roof and celotex to prevent condensation.
 
cables warm up in use. this is normal. as long as the heat can dissipate, there's no problem. covering cables in insulation reduces their current capacity, the derating factor dependent on how thick the insulation over the cables is.e.g. 6mm cable with no insulation is rated at 47A continuous. derating due to insulation can be as much as 40%. a reasonable air gap around the cable is recommended where cable is heavily loaded.
 
cables warm up in use. this is normal. as long as the heat can dissipate, there's no problem. covering cables in insulation reduces their current capacity, the derating factor dependent on how thick the insulation over the cables is.e.g. 6mm cable with no insulation is rated at 47A continuous. derating due to insulation can be as much as 40%. a reasonable air gap around the cable is recommended where cable is heavily loaded.
Because of vaulted ceilings our cable runs in air gaps between insulation and roof, I don’t know building regs for air gap in roof but I believe it minimum 50mm or more. Maybe it is not same as no insulation, but there is good air gap.
 

Reply to DUAL APPLIANCE OUTLET PLATE in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
310
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
932

Similar threads

I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
433
  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
688

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top