Discuss My consumer unit as I want it in the UK Electrical Forum area at ElectriciansForums.net
The 16A MCB is wrong . It is 6 A, sorry. 2 Main switches because I want Shed and outdoor lighting be separate)Why 2 main switches?
You don't get 63mA and 80mA RCDs. I think you are confused with the maximum operating current.
Outside lighting on a 16A MCB - maybe a bit OTT?
I would go for a full RCBO unit with an SPD.
I have made another mistake in writing. These are 80A,63 A and 40A RCDsThe 16A MCB is wrong . It is 6 A, sorry. 2 Main switches because I want Shed and outdoor lighting be separate).
Yes, RCBOs are better, I will have more space as well.I think you'd be better off with a single 100a main switch then use individual RCBOs for all circuits. This would provide better discrimination in the event of an earth fault on any final circuit.
Yes, RCBOs are better, I will have more space as well.
I have uploaded the revised image. I will have a small consumer unit in the shed being fed from here. I am not sure if it is wise to feed the shed CU from a a RCBO in this main CU!?Why 2 main switches?
You don't get 63mA and 80mA RCDs. I think you are confused with the maximum operating current.
Outside lighting on a 16A MCB - maybe a bit OTT?
I would go for a full RCBO unit with an SPD.
I have uploaded the revised image. I will have a small consumer unit in the shed being fed from here. I am not sure if it is wise to feed the shed CU from a a RCBO in this main CU!?
That is a very wide question as it depends on what the shed is for, etc.I am not sure if it is wise to feed the shed CU from a a RCBO in this main CU!?
I think you would be best to get an electrician to give you a quote for this work. This will also ensure the necessary notification side is
The shed is wooden and I will have a CU with a 6A mcb for lighting in there and a 16 Am mcb for a single socket. That is it. I do not think that is a problem at all.That is a very wide question as it depends on what the shed is for, etc.
In the majority of cases (lights & couple sockets) just take it from a RCBO and it is fine.
In the minority of cases (used as a workshop, or big loads like a heated sex pond) then you might want it fed from a separate fuse-switch off the supply tails, but then you have to be sure the cable is safe without RCD protection (so in effect SWA all the way) and the garage CU then has to have a RCD or all-RCBO.
Cable requirements can also be influenced by the earthing arrangement for the supply and any extraneous metalwork at the shed such as metallic water pipes, etc.
But in all of these cases it is not DIY work, and in England and Wales it falls under Part P of the building regulations as notifiable work. Your best plan is to find a good electrician locally who is registered with one of the competent person schemes like NICEIC as they can do the necessary initial design and finally notify their own work without the fees building control normally charge to test & inspect.
Reply to My consumer unit as I want it in the UK Electrical Forum area at ElectriciansForums.net