Hello,

Asking for Friend....

At a two bed house an EICR was carried out and was failed due to no RCD Protection and the buzz bar being exposed.

Another Company has since attended and passed EICR without doing the recommendations.

Where do they go from here. Take the pass or fail.
Obviously safety is priority so why would it have been passed??
 

Attachments

  • [ElectriciansForums.net] EICR
    1339D8B1-7542-4C51-AC7D-74692CC6E1CA.png
    633.3 KB · Views: 49
Before answering. Really shouldn’t have that cover off if still turned on.

difficult to answer without seeing the original test certs.
but, just because the installation has no RCD protection does not mean it’s a fail. Saying that your board does have partial RCD protection.

no buz bar cover Not a fail if it has a good lid over consumer unit. Improvement r3comended only, but there may be more to it than that.

second sparky may be right, but/impossible to comment yet.

post cert on here with details redacted and we will give a better answer.
 
Before answering. Really shouldn’t have that cover off if still turned on.
I suspect they turned off the RCD and did not realise the right hand bus-bar would still be live with the main switch on!

To the OP be very careful and switch off before you try to manipulate the cover back in place!
 
I passed a Classic Wylex filled with 3036's and no RCD last week. My main objective is to make sure the installation is safe......It was safe.
No cover on busbar is okay so long as you have a consumer unit cover.
The only issue I had was when I forgot I was wearing my weekend outfit with dangly metal earrings and a blue beard.........fortunately, for my safety, the customer would not let me in their house.
 

Reply to EICR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
244
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
717
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
686

Similar threads

Definitely, although most likely within the accessories. I've often found that once accessories are disconnected the cabling IR is fine. Sometimes...
Replies
19
Views
2K
I would C2 this, cable is not suitable for the environment its installed in, we would C2 a socket for equipment likely to be used outside , cable...
Replies
11
Views
945

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top