I think it is more that the report is a draft, i.e. not complete. Wouldn't want you to tell the sparks that no serial number means it's invalid as they won't wear that. Being a ground floor flat means that upstairs will have to have floor boards up. Is that viable? ÂŁ640 for a box change is not too bad. Think I would charge more potentially but I like to use good kit which is more expensive. And of course there is the investigative work. Can you get to the flat above?
 
Thank you for all the replies. That has been really helpful. So from what you have all said:
  • 40 year old wiring is not in itself a problem
  • The problem that needs further investigation is the low insulation values, which could be due to something else.
  • Generally there are a lot of mistakes in the report which point to a lack of know how and the fact of not having included the serial number invalidates the report anyway.
  • Would be good to get someone else in to take a look, conduct some end to end testing to work out where low resistance values are coming from. Then think about the next steps without jumping to the full rewire immediately.

The flat is a ground floor flat that has had some problems with damp, could this be the potential root of the issues?
I think you’re Bristol?? Viable for me if you do want a second opinion (caveat being that I’ll be sharing back on here!), DM me if you want.
 
Looking at the EICR it is certainly prepared with a lack of care with no proof reading and is possibly just a badly edited copy of the inspectors previous EICR given things like the circuit numbers don't work for a 6 way CU or the picture of it
 
The flat is a ground floor flat that has had some problems with damp, could this be the potential root of the issues?
Definitely, although most likely within the accessories. I've often found that once accessories are disconnected the cabling IR is fine.
Sometimes the boxes need replacing too where badly corroded but ideally damp proofing first!
 

Reply to EICR - Full rewire recommended in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
829

Similar threads

That is what i am going to do. Thanks mate!
Replies
11
Views
676
This fella puts his face to it about halfway through, he has an opinion on the very subject.
Replies
42
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top