Ok, say you've got a lighting run with the last fixture being 1,280 meters away. 1,800 watts per phase 3 phase, 277/480Y volts though in this example we can use 230/400Y for the ease of discussion.

My question is- what size wire do I run for each phase and earth? What disconnection time do I use? Do I use a Type B, C or D breaker? What should my max R1+R2 come out to be?





[ElectriciansForums.net] Circuit Wire For Long Run
 
Last question- I promise ?

Any idea what the AC R would be at 150*C and 250*C? I'd like to use that as a basis to calc final short circuit conditions.
The basic assumption is copper is fairly linear w.r.t. temperature up to around 1000C (so anything that might be usable for a cable) so you have:

R = R20 * (1 + alpha20 * (t - 20))

Where R20 is the temperature at 20C (e.g. from tables) and alhpa20 is the coefficient at 20C which is around 0.00393 (depending on copper purity and annealing, etc, but not far off this).

So if looking at 250C and the 20C tabulated values for UK cables, then the adjustment factor is:

1 + 0.00393 * (250 -20) = 1.9039

So basically almost double the cold resistance.
 
What about 150*C?
Ummm......

R = R20 * (1 + alpha20 * (t - 20))

Where R20 is the temperature at 20C (e.g. from tables) and alhpa20 is the coefficient at 20C which is around 0.00393 (depending on copper purity and annealing, etc, but not far off this).

So if looking at 250C and the 20C tabulated values for UK cables, then the adjustment factor is:

1 + 0.00393 * (250 -20) = 1.9039

[ElectriciansForums.net] Circuit Wire For Long Run
 
The basic assumption is copper is fairly linear w.r.t. temperature up to around 1000C (so anything that might be usable for a cable) so you have:

R = R20 * (1 + alpha20 * (t - 20))

Where R20 is the temperature at 20C (e.g. from tables) and alhpa20 is the coefficient at 20C which is around 0.00393 (depending on copper purity and annealing, etc, but not far off this).

So if looking at 250C and the 20C tabulated values for UK cables, then the adjustment factor is:

1 + 0.00393 * (250 -20) = 1.9039

So basically almost double the cold resistance.


If curious here is why I ask:



UL and the NFPA are using 25*C for their loop impedance calcs and a Ze of 0.25 ohms.

It is the belief of many electricians that the fault current is universally much higher than 500 amps.

If this is the case, that arc fault coverage reaches much further into the circuit. If we can prove that to be the case, much of 210.12 is nullified.




[ElectriciansForums.net] Circuit Wire For Long Run



[ElectriciansForums.net] Circuit Wire For Long Run



There is more, but thats the general part of it.
 
Last edited:

Reply to Circuit Wire For Long Run in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
I appreciate the input on this. I decided it is not a good idea, and will spend the money and time to install a new dedicated circuit with...
Replies
5
Views
1K
  • Question
This contactor you suggested unfortunately only has two NO switches rather than 1 NC and 1 NO required for the CR3 current sensing bypass...
Replies
14
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2
Replies
45
Views
5K
  • Question
Hi There How did you get on with your basement project?
Replies
1
Views
971
  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks