Boiler Switch | on ElectriciansForums

Discuss Boiler Switch in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jan 23, 2021
Messages
21
Reaction score
3
Location
UK
Hi

We are having a new kitchen installed and have changed ll the sockets / switches to a stainless steel (Like below)


There is a boiler switch below the boiler which i cant seem to find a switch for. Can i just use a fused spur? any advise would be great. I have found 3 pole switches but they all say "fan isolation" on them

[ElectriciansForums.net] Boiler Switch
[ElectriciansForums.net] Boiler Switch
[ElectriciansForums.net] Boiler Switch
 
You might need to get an electrician to trace what all the cores are doing.
Normally there is just a switch fuse that isolated the entire heating system.

I don’t think I’ve ever seen a 3 pole isolator on boiler circuits??
 
I suspect the 3 pole switch has been used to replace a programmer that would have originally been there.
The simplest fix is to fit another 3 pole fan isolator.

If the adjacent spur is the sole supply to the heating system (can't see any sideways interconnection) or if there is a single spur supplying the heating elsewhere, then the 3 pole could probably be eliminated by using connectors then just have a blank fitted over, checking would be required.
 
Last edited:
T
I suspect the 3 pole switch has been used to replace a programmer that would have originally been there.
The simplest fix is to fit another 3 pole fan isolator.

If the adjacent spur is the sole supply to the heating system then the 3 pole could probably be eliminated by using connectors then just have a blank fitted over, checking would be required.
Hi

So that is a 3 pole switch? ill just buy one that says Fan its thats the case
 
T

Hi

So that is a 3 pole switch? ill just buy one that says Fan its thats the case
You might be able to find one that has no writing on it.

As suggested above though... if the 3 pole isolator isnt actually doing anything... (do you turn it on and off frequently? is the whole heating system also isolated elsewhere?) then you could joint through each switch and cover with a blank plate in the decoration you need...

Advise: If your changing these to metal, then you might need to earth the plate
 
You might be able to find one that has no writing on it.

As suggested above though... if the 3 pole isolator isnt actually doing anything... (do you turn it on and off frequently? is the whole heating system also isolated elsewhere?) then you could joint through each switch and cover with a blank plate in the decoration you need...

Advise: If your changing these to metal, then you might need to earth the plate
I've purchased the below. Will this be ok do you think ?

 
I've purchased the below. Will this be ok do you think ?

 
I've purchased the below. Will this be ok do you think ?

need a perfect skim on the wall.perfectly flat or your switch will keep falling off. flatplate.... spawn of the devil.
 
Provided it's wired to simply call for heat/water or not, which is most likely, then that 10A switch is fine - most heating programmers only have contacts rated at 3amps anyway.

It would be interested to know if there's a fused spur elsewhere for the boiler, and whether it has a wireless programmer/time clock as many do these days. Do you ever use that switch?
 
It will be to isolate the boiler locally, assume the heating controls and wiring Centre are elsewhere with their own isolator. So there will be a permanent live, neutral and a switched live for the boiler. That 3 pole isolator most likely is to disconect those 3.

EDIT although looking at the photo again, I'm not so sure.....
 
Last edited:
I'm not 100% sure either. I'm not sure any of us can be without a closer look at what's going on there.
But In a sense it only matters either way if the switch rating matters.

Permit me to ask a silly question which I accept I should know the answer to:
Are you allowed to stick a 10amp rated switch on a (probably) 13A fused spur with a known load on the basis that it will never draw anything approaching 10amps most of the time (fan and pump really) and the switch would only have to survive long enough in fault conditions to blow the upstream fuse. A similar principle to 433.1.1. But I can't recall ever noting this being allowed. I also don't have BBB here to consult and my default position would be "no".
Anyone?!

(I also note that triple pole 20 amp switches marked boiler are practically non existent, though there are double pole 20 amp ones out there. )
 
I'm not 100% sure either. I'm not sure any of us can be without a closer look at what's going on there.
But In a sense it only matters either way if the switch rating matters.

Permit me to ask a silly question which I accept I should know the answer to:
Are you allowed to stick a 10amp rated switch on a (probably) 13A fused spur with a known load on the basis that it will never draw anything approaching 10amps most of the time (fan and pump really) and the switch would only have to survive long enough in fault conditions to blow the upstream fuse. A similar principle to 433.1.1. But I can't recall ever noting this being allowed. I also don't have BBB here to consult and my default position would be "no".
Anyone?!

(I also note that triple pole 20 amp switches marked boiler are practically non existent, though there are double pole 20 amp ones out there. )

Don't forget you use 20 Amp switches in kitchens for example. What's the OCPD rating in that case?
 
Don't forget you use 20 Amp switches in kitchens for example. What's the OCPD rating in that case?
That actually doesn't feel the same...
20amp switch then 13A fuse (either in plug or FCU) then appliance. Current through switch is limited to below it's rating.
I think this would potentially be 13amp fuse, 10 amp switch in middle, then appliance? Current through switch not limited to below it's rating?
 
That actually doesn't feel the same...
20amp switch then 13A fuse (either in plug or FCU) then appliance. Current through switch is limited to below it's rating.
I think this would potentially be 13amp fuse, 10 amp switch in middle, then appliance? Current through switch not limited to below it's rating?

True yes. I'll have another think!
 
Provided it's wired to simply call for heat/water or not, which is most likely, then that 10A switch is fine - most heating programmers only have contacts rated at 3amps anyway.

It would be interested to know if there's a fused spur elsewhere for the boiler, and whether it has a wireless programmer/time clock as many do these days. Do you ever use that switch?
Hi

No never really use the switch. When we moved in it had a programmer by the boiler and a analogue dial by the front door.

We have since installed Hive. Bit annoying as I've had to get a switch that says "Fan Isolator"
 
I'm not 100% sure either. I'm not sure any of us can be without a closer look at what's going on there.
But In a sense it only matters either way if the switch rating matters.

Permit me to ask a silly question which I accept I should know the answer to:
Are you allowed to stick a 10amp rated switch on a (probably) 13A fused spur with a known load on the basis that it will never draw anything approaching 10amps most of the time (fan and pump really) and the switch would only have to survive long enough in fault conditions to blow the upstream fuse. A similar principle to 433.1.1. But I can't recall ever noting this being allowed. I also don't have BBB here to consult and my default position would be "no".
Anyone?!

(I also note that triple pole 20 amp switches marked boiler are practically non existent, though there are double pole 20 amp ones out there. )
But what rating is your OCPD at the board? 6A for heating?
 
Well now I'm lost lol

I have purchased a 3 pole fan 10amp switch.

It seems to have the same outputs L1 L2 etc...

Next to the boiler is the Hive box which I'm sure is wired into this switch then up to the boiler. I could be wrong.

Would any more photos help?
 
I'll give it a go. It was more making sure I have the correct switch. Any tips for getting the lettering off

We have some BG brushed accessories as they were the only brand that offered grey inserts, rather than the usual option of black or white.

Much better quality than I had expected, but lettering started to disappear from cooker switch and that very same 3 pole isolator (used for the very same purpose) about the third time my other half wiped them with a cloth. I quickly finished the job with a thumb nail.
 
But what rating is your OCPD at the board? 6A for heating?
We don't have that information. If so, I agree absolutely no problem. But the boiler spur might equally be on a 16A radial or on the RFC.
Well now I'm lost lol

I have purchased a 3 pole fan 10amp switch.

It seems to have the same outputs L1 L2 etc...

Next to the boiler is the Hive box which I'm sure is wired into this switch then up to the boiler. I could be wrong.

Would any more photos help?
Sorry If I added confusion. The potential issue is just how much current the switch is designed to handle. Not so much about whether the boiler will overload it, more whether the regs allows a 10amp switch on a supply that is potentially fused higher.
Do you know which circuit breaker or Fuse isolates the boiler at your consumer unit? Does it have it's own breaker or Fuse or is it part of a plug sockets circuit?
 
We don't have that information. If so, I agree absolutely no problem. But the boiler spur might equally be on a 16A radial or on the RFC.

Sorry If I added confusion. The potential issue is just how much current the switch is designed to handle. Not so much about whether the boiler will overload it, more whether the regs allows a 10amp switch on a supply that is potentially fused higher.
Do you know which circuit breaker or Fuse isolates the boiler at your consumer unit? Does it have it's own breaker or Fuse or is it part of a plug sockets circuit?m

We don't have that information. If so, I agree absolutely no problem. But the boiler spur might equally be on a 16A radial or on the RFC.

Sorry If I added confusion. The potential issue is just how much current the switch is designed to handle. Not so much about whether the boiler will overload it, more whether the regs allows a 10amp switch on a supply that is potentially fused higher.
Do you know which circuit breaker or Fuse isolates the boiler at your consumer unit? Does it have it's own breaker or Fuse or is it part of a plug sockets circuit?
It has one on the circuit breaker picture attached

[ElectriciansForums.net] Boiler Switch
 

Attachments

  • [ElectriciansForums.net] Boiler Switch
    20210423_080722.jpg
    197.6 KB · Views: 15

Reply to Boiler Switch in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Electric combi boilers are not as effevtive to heat flowing water compared to gas. I'd only consider an electric combi if you lived in the middle...
Replies
4
Views
411
  • Question
Thanks, it says under the picture of the 4 front plates (in the tiniest writing possible) "Excluding the definity grid pro front plates which do...
Replies
5
Views
657
N
  • Question
In my first sparking era (late 90's) I was always told to run a neutral to the isolator, as the chances are whoever is using the machine will...
    • Like
Replies
21
Views
1K
  • Question
You need a wi fi switch that is compatible with your switchbot thermostats. Remove the SCR, use the neutral and live to power the wifi switch, and...
Replies
8
Views
728
  • Question
There's some stunning Chinglish on that data plate
    • Optimistic
Replies
19
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks