wholesalers mcb | on ElectriciansForums

Discuss wholesalers mcb in the UK Electrical Forum area at ElectriciansForums.net

Joined
May 4, 2021
Messages
21
Reaction score
18
Location
NI
Im looking to put a supply out in a mancave, the earthing arrangement is tns. At the supply there is iscos installed so I was going to take a supply out of the iscos into a 40 amp DP MCB and run a 6mm T+E surface piped along an outside wall. I will be installing a 40A 30mA RCD in the mancave. My query is the wholesalers dont stock 40 amp double pole MCB's, I cant find anything wrong with what im planning in the regs.
The fact the wholesaler doesnt stock them has sorta through me a bit. Do I need to protect the supply cable with an RCD in the house aswell.
Thanks in advance.
 
T/E is not advisable outdoors. best use SWA. could start with T/e indoors and then switch to SWA in adaplable box. making sure that the armour is earthed, even if not used as cpc. RCD at supply end only needed if the first section of T/E is buried < 50mm deep in wall/s. you could start with a 40A S/P MCB into a D/P switch
 
T/E is not advisable outdoors. best use SWA. could start with T/e indoors and then switch to SWA in adaplable box. making sure that the armour is earthed, even if not used as cpc. RCD at supply end only needed if the first section of T/E is buried < 50mm deep in wall/s. you could start with a 40A S/P MCB into a D/P switch
point noted about the cable type. I will have to install a 3 module cu with a 80a DP MCB and a 40a SP MCB.
 
It's not ideal to use a MCB at the house end of the cable. It may switch off at the same time as a lower rated MCB in the shed when a fault occurs. A switch/fuse, such as the one in my link, gives better discrimination, and will take a SWA gland direct.
 
It's not ideal to use a MCB at the house end of the cable. It may switch off at the same time as a lower rated MCB in the shed when a fault occurs. A switch/fuse, such as the one in my link, gives better discrimination, and will take a SWA gland direct.
too expensive and space my be an issue. I prefer this with a 45A fuse.:

[ElectriciansForums.net] wholesalers mcb
 

Reply to wholesalers mcb in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
634
  • Question
This charger doesn't support rear entry from the looks, only bottom entry, hence that. Unless they make a white sheathed SWA, I would still need...
Replies
8
Views
961
As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
1K
  • Question
You need a CT clamp at main tails, it depends on the rules where you are - you used to be allowed wireliss ones (such as MyEnergi Harvi), these...
Replies
14
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks