I was asked to "just fit a bigger breaker" by a plumber who had installed an electric shower for a customer. Bit surprised he hadn't finished the task but I arrived with a DIN rail full of conventional, spring fitted MCB's. I've seen a fair amount of old kit (East London rentals are full of the stuff) but this was new to me. I've suggested / quoted either a new CU or an external housing with an isolator and RCBO but I'd be interested to know what this was if one of the more experienced heads could identify it. Two images attached. Thanks guys.
 

Attachments

  • [ElectriciansForums.net] Identifying an old Wylex CU Breaker
    20210514_093510.jpg
    251.9 KB · Views: 44
  • [ElectriciansForums.net] Identifying an old Wylex CU Breaker
    20210514_093513.jpg
    227.5 KB · Views: 43
Will be stripping three of these boards out in the next few weeks and and combining them in a two tier, SPD and all RCBO hager board.

Looking at 18- 20 circuits, sadly none above 32A.

Is there any value in this Stuff?
 
Will be stripping three of these boards out in the next few weeks and and combining them in a two tier, SPD and all RCBO hager board.

Looking at 18- 20 circuits, sadly none above 32A.

Is there any value in this Stuff?
For the unusual sizes yes people like this will buy them from you albeit not for what they are selling them at.
 
I think I’ve got a bucket of old breakers.....


quick rake through the van, found MEM. Are these compatible? Might still have Wylex ones in my store.

[ElectriciansForums.net] Identifying an old Wylex CU Breaker[ElectriciansForums.net] Identifying an old Wylex CU Breaker
 
Last edited:
I think I’ve got a bucket of old breakers.....


quick rake through the van, found MEM. Are these compatible? Might still have Wylex ones in my store.

View attachment 85990View attachment 85991
That's interesting and looks very similar although one of my fears is, as mentioned above, will the thirty year old RCD work and would you trust your reputation or their life to it? Brilliant answers - I may print this and thread and show it to the client whom, I suspect, is wondering why a simple breaker has now gone up ten fold in price (thanks Mr Plumber)!
 
Last edited:
Just looks through my old breakers and have many 30As but nothing above. This is the difference between the breaker @littlespark showed and the Wylex one, the busbar fitting is a different height and don't really fit.[ElectriciansForums.net] Identifying an old Wylex CU Breaker
 
Interestingly, quoted the the client with a follow-up to "explain why the "half hour for the sparky to fit a breaker" the plumber had promised before disappearing, had morphed into a board change or external RCD. The client reported "all sorted"! my suspicion is an unsafe connection to the shower but I've done my best.
 
Wont be long until you're back out to do the job properly.

When that happens, be sure to charge plenty to make up for the messing about.
My old boss had a code for jobs like that. When pricing up he’d say to me ‘This one might be TT’
TT stood for To55er Tax.
 
Just found a Wylex NB40 in the shed @Marti
Doesn't sound like you need it now, but if the silly customer decides to be safe and get the job done properly then let me know and I'll send it on.
 
Just found a Wylex NB40 in the shed @Marti
Doesn't sound like you need it now, but if the silly customer decides to be safe and get the job done properly then let me know and I'll send it on.
Much appreciated. Thank you for going to so much trouble. Less concerned about getting the job but would like to know this client is safe; even from her own decision making.
 
4mm multi! Not much use for anything except as a draw wire for a bit of 10mm T&E. Something else the plumber skipped when he fitted a 9Kw Triton on the old cable.
Have had a 8.5Kw in 4mm hanging off a B32 in my place for about 10 years, haven't got round to rewiring it....Its fine...it is just me though and I don't wash that often...
 

Reply to Identifying an old Wylex CU Breaker in the Electrical Engineering Chat area at ElectriciansForums.net

Similar Threads

  • Question
Absolutely, yes. It was just a bit of a joke, looking at your quoted Z values. edit. Oh, joking too!.....I see your attempted smile didn't work ...
2
Replies
28
Views
6K
Horrible, old and when working through it, in my hair!
2
Replies
34
Views
6K
  • Question
I recently signed up to the looped energy app. It's currently free and just gives you the energy readings from the smart meter every 30mins.
Replies
24
Views
7K
And let's be honest here, big commercial properties serving several floors of offices, badly marked up db and you have to add a radial in to a...
Replies
17
Views
3K
  • Question
there is no built in timer, the timer is in a separate photo. I wouldn't call it a monstrosity, looks like it was originally installed to a good...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks