I recently inspected a job in a 1960s-era apartment building. Three of the properties have old Wylex rewireable consumer units (CUs) with Pyro wiring.

To minimize damage to the 50-year-old Pyro, which passed testing, I propose the following approach:

1. Utilize the old CU as a junction box.
2. Remove the internal components and install a DIN rail.
3. Extend the cables using DIN rail connectors.
4. Construct a wooden support in front for the new consumer unit.

I welcome your thoughts and suggestions.
 
Construct a wooden support in front for the new consumer unit.

I suppose you are doing this as there is no room to fit the new CU adjacent to the old one? It's just that the new one is going to be sticking out quite a bit, if its in front of the old one.
 
I suppose you are doing this as there is no room to fit the new CU adjacent to the old one? It's just that the new one is going to be sticking out quite a bit, if its in front of the old one.
Limited space. It is in a cupboard. So they'll lose a bit of cupboard space.
 
If you are rendering the DIN rail inaccessible in normal use then it needs to be maintenance free.
 
I recently inspected a job in a 1960s-era apartment building. Three of the properties have old Wylex rewireable consumer units (CUs) with Pyro wiring.

To minimize damage to the 50-year-old Pyro, which passed testing, I propose the following approach:

1. Utilize the old CU as a junction box.
2. Remove the internal components and install a DIN rail.
3. Extend the cables using DIN rail connectors.
4. Construct a wooden support in front for the new consumer unit.

I welcome your thoughts and suggestions.

I have done similar in the past, although it was side by side, not one on top of the other.

2 suggestions, they may / may not be suitable for the space available.

1
the lid of the old fuse box will have big holes in it when you have removed the fuse gear and main switch
I have screwed / pop riveted an aluminium sheet over the face of old boards in the past to seal up the big holes in the front.

2
when you construct the wooden support, use a sheet of ply on the front of it to mount the new board to.
pass the cables through the rear entry of the new board through a hole drilled in the ply.
use a couple of hinges on the bottom of the ply and then screw the top to the batons.

If you need to get behind it to fault find or check any of the cables / joints, you can undo the top screws and fold the new board down to access behind it.
 
I have done similar in the past, although it was side by side, not one on top of the other.

2 suggestions, they may / may not be suitable for the space available.

1
the lid of the old fuse box will have big holes in it when you have removed the fuse gear and main switch
I have screwed / pop riveted an aluminium sheet over the face of old boards in the past to seal up the big holes in the front.

2
when you construct the wooden support, use a sheet of ply on the front of it to mount the new board to.
pass the cables through the rear entry of the new board through a hole drilled in the ply.
use a couple of hinges on the bottom of the ply and then screw the top to the batons.

If you need to get behind it to fault find or check any of the cables / joints, you can undo the top screws and fold the new board down to access behind it.
Like the idea of hinging the ply. It was in the back of my mind that if there is a fault back there it would be a nightmare.

I was planning to bung the holes, and screw a blank plate over the main switch. But I like your idea better.
 
My main concern is it's rough 🤣..
Not Really, done similar myself, I don't personally like the wood part of the post though, is there any other material you could use which is flame/ fire proof/ that said I have seen wood used before also, and PYRO is good stuff, last forever.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Horleyy
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Business Name
MSE

Thread Information

Title
Would you use an old CU to extend cables.
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
8

Thread Tags

Advert

Thread statistics

Created
MJS_84,
Last reply from
Taylortwocities,
Replies
8
Views
847

Advert

Back
Top