Good afternoon all,
Our company installs fire alarm systems in convenience stores but it's always limited to a conventional system whether it be 2, 4 or 8 zones.
However, a store has come up where the existing alarm panel is in a communal area of the building.
The existing panel is a 32 zone C-Tec XFP panel and we are looking to install a 4 zone C-Tec CFP panel.
I have been advised by C-Tec that we would require a SA4700-102 to link the CFP panel to the XFP panel so that the XFP panel will show a fault in a specified zone when the CFP panel has a fault/fire alert.
The problem is we have never had a store where we have had to do this so I want to make sure I've been advised the correct part and I'm also looking for advise on what connections to use at both ends if anyone can offer that?
Apologies for the ignorance but unfortunately its just not something I've ever had to do before and I've got to learn somewhere I guess!
Thanks for your help in advance.
Our company installs fire alarm systems in convenience stores but it's always limited to a conventional system whether it be 2, 4 or 8 zones.
However, a store has come up where the existing alarm panel is in a communal area of the building.
The existing panel is a 32 zone C-Tec XFP panel and we are looking to install a 4 zone C-Tec CFP panel.
I have been advised by C-Tec that we would require a SA4700-102 to link the CFP panel to the XFP panel so that the XFP panel will show a fault in a specified zone when the CFP panel has a fault/fire alert.
The problem is we have never had a store where we have had to do this so I want to make sure I've been advised the correct part and I'm also looking for advise on what connections to use at both ends if anyone can offer that?
Apologies for the ignorance but unfortunately its just not something I've ever had to do before and I've got to learn somewhere I guess!
Thanks for your help in advance.