Hi, Ive had a NAPIT qualified electrician out to install a new feed to the garage along with a new consumer unit in there. Its a short distance of around 6m and the cable he used was a 16mm NYY cable, it has been directly buried around 300mm depth with yellow warning tape, It goes under a few paving slabs but mostly its a graveled area.

Is this installation totally 100% in accordance with current building regulations/standards?

When he came to quote I asked for armored cable, he even specced SWA in the written quote but on the day I noticed it was this NYY cable. He said its all OK and he has passed the Part P certificate onto my local authority. When I questioned him after the job he said its easier to use and bend and things have changed over the years and this cable is fine to use in the installation. He said there is no price difference too.

What are people's thughts?
 
Hi, he has been and done the work replacing with SWA. I told him about the BS7671 and what NAPIT said but he just murmerred something about no traffic over the ground.

Just another question. He has not earthed the actual armouring part of the cable. It is a 3 core cable which one is earth. Should the armouring be earthed too?
 
Hi, he has been and done the work replacing with SWA. I told him about the BS7671 and what NAPIT said but he just murmerred something about no traffic over the ground.

Just another question. He has not earthed the actual armouring part of the cable. It is a 3 core cable which one is earth. Should the armouring be earthed too?

Is this an electrician doing the work?
 
There's always a chance he has earthed it. The OP would need to check both ends of the cable and know exactly what they were looking for. In addition, I sometimes bend the banjo inside the plastic junction box, so the little nut and bolt may not even be on view.
Firm evidence needed before the chap is condemned again. Plus, I'm not advising the OP starts undoing electrical items to take a look unless he 100% knows what he's doing and switches all power off first.
 
[ElectriciansForums.net] NYY Buried Cable - Legit job?


The Hager was installed a few years ago when we had AC installed. The consumer box to the garage is the larger SWA. He could not terminate into the Hager hence the plastic box. It does look like there is an earth wire from the gland.
 
Blue crimp on 4mm2? PVC insulating tape on joints? Equipment in DNO box?
It's not great is it? I paid £875 for this installation too. There was a bit of fiddling around in the garage too connecting the sockets and lighting circuit . He was here for 5 hours on the first visit then 2 hours replacing cable to SWA, I was expecting a thorough 2 days for that price. He is a definite NAPIT registered electrician. He had such a well-organised van as well! I had high hopes. He gives NAPIT a bad name, goes without saying he will not be used again by me nor recommended.
 
It is rough but the armour would appear to be earthed. That adaptable box in the meter cupboard could have been mounted externally butted up to the cupboard with the swa into the bottom. Who connected up the garage consumer unit as those cpcs look pretty rough and as above that blue crimp is not suitable for 4.0.
 
It is rough but the armour would appear to be earthed. That adaptable box in the meter cupboard could have been mounted externally butted up to the cupboard with the swa into the bottom. Who connected up the garage consumer unit as those cpcs look pretty rough.
I did not want that plastic box on the wall, this meter is right next door my front door I told him to put that in the meter box. He said it was too difficult to terminate straight into that Hager. Either that or he couldn't be bothered.
 
I did not want that plastic box on the wall, this meter is right next door my front door I told him to put that in the meter box. He said it was too difficult to terminate straight into that Hager. Either that or he couldn't be bothered.
It would not have been easy to get the swa into the Hager board and without physically being there it is difficult to judge. If it were me doing the job the box would have been external to the cabinet whether the client liked it or not.
 
It's earthed both ends. The garage end is metal box and has earthing nut. The source end is a bit rough.
But if he was told he can't put the box on the wall I have more sympathy.
I agree with him that I wouldn't want to be getting the SWA into the existing Hager - the bottom face is the only option and it looks too busy.
 
Last edited:

Reply to NYY Buried Cable - Legit job? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Sounds more positive.
Replies
8
Views
472
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
489
  • Question
This is so true...look at the client and what they want to achieve. sometimes what they want is outwith budget/common sense...but they expect you...
    • Like
    • Agree
Replies
2
Views
1K
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
1K
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks