Hi, Ive had a NAPIT qualified electrician out to install a new feed to the garage along with a new consumer unit in there. Its a short distance of around 6m and the cable he used was a 16mm NYY cable, it has been directly buried around 300mm depth with yellow warning tape, It goes under a few paving slabs but mostly its a graveled area.

Is this installation totally 100% in accordance with current building regulations/standards?

When he came to quote I asked for armored cable, he even specced SWA in the written quote but on the day I noticed it was this NYY cable. He said its all OK and he has passed the Part P certificate onto my local authority. When I questioned him after the job he said its easier to use and bend and things have changed over the years and this cable is fine to use in the installation. He said there is no price difference too.

What are people's thughts?
 
Another no vote from me, sorry. There has been a misunderstanding of the Regulations to think unarmored cable is suitable for direct burial.
Also it is often not clear from the cable suppliers that this is the case, for example here it has no mentioned of the BS wiring regs:
"NYY-J Cable is a non armoured mains cable that can be installed indoors where there is little chance of mechanical damage. It can be installed in open air, underground, in water and also in brickwork and concrete with the exception of shaken, vibrated or compressed concrete."

Where has here they say the cable is suitable for direct burial in many cases, but point out the BS regs don't allow it without additional physical protection:
"These are widely used European power and control cables designed for fixed wiring installation with a voltage rating of 600/1000V. They can be safely deployed in most applications where mechanical stresses are not anticipated – indoors, outdoors, direct burial underground, in concrete, or submerged in water. When NYY cables are required to comply with the UK wiring regulations BS7671 for burial in the ground, they require installation in a conduit or duct to provide protection against mechanical damage. They are not suitable for installation in concrete which is shaken, vibrated or compressed."

The armour of SWA is not just for mechanical protection. In the event of a cable penetration accident with a spade, pick, mechanical digger, etc, it serves to short out the supply and cause it to disconnect on the over-current protection (supply fuse or MCB). Often such sub-mains do not have RCD protection as it is down-stream in the garage CU, etc, making that a very important point.
 
Last edited:
Give him a chance to report the guy!

It was late last night that the 100% confirmation that this is wrong, and most people sleep overnight.

He may give the electrician one more chance to put right (all correspondences in writing!) before going to NAPIT.
 
Give him a chance to report the guy!

It was late last night that the 100% confirmation that this is wrong, and most people sleep overnight.

He may give the electrician one more chance to put right (all correspondences in writing!) before going to NAPIT.

I know what you mean, but also read post 8.
 
Yes. I read #8, and no reply from him since then, even though there was plenty input from the forum.

I’m hoping he is thinking about it, and will confront the spark ASAP.

I just don’t think we should assume he’s ignoring us just because he hasn’t replied from 7pm yesterday. You never know, he might have a life that doesn’t involve sitting on a forum all night.

All I’m saying is wait a few days. ?
 
I've been thinking of playing devils advocate and trying to come up with reasons why it may possibly be ok.... but I can't think of any.

It needs to have mechanical protection in order to comply with BS7671.

Chances are it may be fine under slabs and gravel, but that's not really the point. It's a bit like saying it'll probably be fine if you drive around without a seatbelt, probably will be, but you wouldn't do it for various reasons.

I feel uncomfortable judging about someone who I have never met, and only hearing one side of the story. We may be missing something. @OsramMyers I would ask for a copy of his complaints procedure which is mandatory to have for a registered electrician. I would then follow that procedure. As part of that process you could ask him to change the cable. If he again says it's ok to use you can then quote regulation 522.8.10 (from BS7671) which clearly shows it is not acceptable in its present state.
 
Yes. I read #8, and no reply from him since then, even though there was plenty input from the forum.

I’m hoping he is thinking about it, and will confront the spark ASAP.

I just don’t think we should assume he’s ignoring us just because he hasn’t replied from 7pm yesterday. You never know, he might have a life that doesn’t involve sitting on a forum all night.

All I’m saying is wait a few days. ?
Eh? ?
 
Update -

Thank you for all the replies. I have dropped an email just a moment ago to NAPIT via their website and will await their response.
When you hear back from them @OsramMyers , could you let us know their reply please? We like updates ?.
 
Update:

Spoke to NAPIT on the phone and the installation is fine. Because its 300mm deep and its a tough cable its OK. Bit shocked really.

I've asked the electrician to replace it all with SWA anyway as outlined in the quote.

Strange, NAPIT seem to be over cautious on certain other things.

Good that the sparky is going to come back to correct things though. Thanks for the update.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Northampton
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
NYY Buried Cable - Legit job?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
73
Unsolved
--

Advert

Thread statistics

Created
OsramMyers,
Last reply from
MJPD29,
Replies
73
Views
18,123

Advert

Back
Top