Fitted 2 new external lights onto existing cabling, their on a remote wall quite a distance from house.
My mistake was not doing a Zs before I started the works.
Finished & tested Zs reading 14 ohms.
Its a Tncs supply quite a big install…the lights are supplied by a 6 amp C type MCB.
Reported this to the Client & my Boss…still no feedback on what to do.
I”ve suggested a Rcbo to protect this circuit & FI TO take place.
Windering your thoughts on this.
 
Fitted 2 new external lights onto existing cabling, their on a remote wall quite a distance from house.
My mistake was not doing a Zs before I started the works.
Finished & tested Zs reading 14 ohms.
Its a Tncs supply quite a big install…the lights are supplied by a 6 amp C type MCB.
Reported this to the Client & my Boss…still no feedback on what to do.
I”ve suggested a Rcbo to protect this circuit & FI TO take place.
Windering your thoughts on this.
What other tests have you carried out? why a C type mcb?
 
Have you done a Ze and dead testing of the circuit as you need to confirm if 14 ohm is actually a realistic reading for the circuit before you fit an rcbo which may be an inappropriate course of action.
Agree but @ this moment there is no earth protection on that circuit.
Or never ever been any earth protectio….regarding the high loop impedance.
 
1 - Are you happy with the earthing in general? You need to be sure that the supply is fine before you consider the circuit. Hence request to do Ze or at a minimum if you can't isolate Zs@DB.

2- Is it realistic that you have (quick smoke packet maths) around 300m of 1mm or almost 500m of 1.5mm on this circuit?
 
Regarding the high loop impedance
 

Attachments

  • [ElectriciansForums.net] Zs reading high on external lighting
    E068C0EB-78E8-4760-AC17-C7784C6AB901.jpeg
    86.2 KB · Views: 53
1 - Are you happy with the earthing in general? You need to be sure that the supply is fine before you consider the circuit. Hence request to do Ze or at a minimum if you can't isolate Zs@DB.

2- Is it realistic that you have (quick smoke packet maths) around 300m of 1mm or almost 500m of 1.5mm on this circuit?
Not sure about the length of circuit. this was a like for like replacement I’ve done all I can reported to all…asked for existing Certification & basically no feedback whatsoever.
Im not happy with the Zs & suggested an Rcbo to give protection & FI will be required.
 
This needs a sample of R1+R2 readings on the circuit at various points along it. Even 2 or three more would tell you a lot.
Unless it's truly a giant circuit and the readings progressively increase along it's length there is probably loose connection somewhere.
(If it really is a circuit that big I'd also be running some volt-drop calculations, it may not comply with max 3% volt drop on lighting circuits.)
 
There is exceeding a protective devices capability and there is exceeding it due to a circuit fault. Can you not see 14 ohm is indicating a fault which cannot be ignored by fitting an rcbo. Did you loop between line and neutral.
 

Reply to Zs reading high on external lighting in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
644

Similar threads

You would be best checking all connections as it is possible it is having a cumulative effect.
Replies
5
Views
370
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top