Fitted 2 new external lights onto existing cabling, their on a remote wall quite a distance from house.
My mistake was not doing a Zs before I started the works.
Finished & tested Zs reading 14 ohms.
Its a Tncs supply quite a big install…the lights are supplied by a 6 amp C type MCB.
Reported this to the Client & my Boss…still no feedback on what to do.
I”ve suggested a Rcbo to protect this circuit & FI TO take place.
Windering your thoughts on this.
Personally I'd stick the live in the earth bar, open up a few car park lights, measure R1+R2 and form a picture of where the resistance jumps high. It shouldn't take that long to get a better understanding of what's going on.
Leaving the live in the earth bar is also an option I'd prefer to installing an RCBO. Leaving part of the circuit functional is also an option if you find good Zs for part of it, while the remainder is investigated more.
You need to talk to your boss again about this. Mistakes happen. He or she will know that.
Yes the Swa been in some time, 2 core only,armourping used for cpc.
that is most likely the problem. as someone has already stated, corroded armour. also depends on if the SWA has been correctly glanded in the first place, not just bodged. definitley needs investigation.
Reply to Zs reading high on external lighting in the UK Electrical Forum area at ElectriciansForums.net
You would be best checking all connections as it is possible it is having a cumulative effect.
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.