No spare ways in the consumer unit. There are two low current radials on their own RCBOs. Do the regs forbid putting the two radials onto the same RCBO - that is two L wires into the one RCBO?
 
I thought we'd laid this one to rest a couple of months ago!
Doesn't matter how many wires from however many radials connect to one MCB or RCBO, as long as their total cross sectional areas doesn't exceed the maximum capacity of the device's terminal and they are all properly secured. They will all form ONE circuit in total.
Connecting multiple radials like this can make fault finding much easier. The last case of RCD tripping I sorted out was caused by a lighting circuit with six individual wires connected to the MCB. Within ten minutes of arriving at the property I'd identified the wire with the poor IR, connected the other five back up, been around the house to see what didn't work,and discovered it was the feed to the light in a boiler house.
Problem was a leak in the shower in the room above directly above the conduit to the switch.
 
Last edited:
@brianmoooore I agree in this case, and must have missed the previous thread on this.
Out of interest, would your comment mean that 314.4 can never actually be broken if combining radial circuits?
 
The idea is to make a way for an SPD by joining two circuits. The SPD will be a single way unit. The BG SPD looks OK. Can it fit into a Wylex CU?


[ElectriciansForums.net] two radials into an RCBO
 
By the letter of the regs. , no, but it depends if you're an engineer or a sheep. I have no problem mixing different makes in a full DIN rail CU, as long as they fit properly.
This doesn't connect to the busbar, so no pulling out of shape. The only possible issue is to make sure the front part projects through the front panel enough to meet the IP rating, which it almost certainly will.
 
I'd make one more comment - perhaps the reason the boiler and the fridge were on separate radial circuits was because they are either (a) somewhat important circuits that could be problematic if tripped, or (b) the loads (at least the boiler or associated valves/pump) are prone to faults. I know most properties don't provide that luxury, pity to take it away.
 
Whenever I swap out a board I look to put everything on its own OCPD and leave space for expansion, so there's often more breakers than the original board.

However if I come to a full board, needing a low power radial, I'll always put it to the customer that I can do a "Spur at source" (which some electricians frown on) or I can put in a new board and a dedicated OPCD.

Guess which option they choose.
 
You certainly can if you like, but it's not actually required as per other posts as it is legitimately one final circuit with a branch.
There isn't a right answer here - we'd all prefer not to add joints if not required, and we'd prefer not to stick two legs in an RCBO.
I'd probably gravitate to the latter option personally.
It would also give DP isolation to an integrated fridge.
 
Is this Wylex single module type 2 SPD of any interest:
It is a bus-bar connection too....no breaker needed for it
 
I'd make one more comment - perhaps the reason the boiler and the fridge were on separate radial circuits was because they are either (a) somewhat important circuits that could be problematic if tripped, or (b) the loads (at least the boiler or associated valves/pump) are prone to faults. I know most properties don't provide that luxury, pity to take it away.
People like a fridge on their own circuits so if another circuit is at fault the fridge is not taken out,
 
Is this Wylex single module type 2 SPD of any interest:
It is a bus-bar connection too....
The Wylex is ÂŁ70 (taking the mick) to BGs ÂŁ38. If two radials are joined there is another way available. Not sure if the BG will fit a Wylex.
 
The Wylex is ÂŁ70 (taking the mick) to BGs ÂŁ38. If two radials are joined there is another way available. Not sure if the BG will fit a Wylex.
In my experience it's usually the bus bar alignment that is the biggest issue, which as someone said wouldn't apply to an SPD which connects to an MCB.
 
By the letter of the regs. , no, but it depends if you're an engineer or a sheep. I have no problem mixing different makes in a full DIN rail CU, as long as they fit properly.
This doesn't connect to the busbar, so no pulling out of shape. The only possible issue is to make sure the front part projects through the front panel enough to meet the IP rating, which it almost certainly will.
The BG can fit onto a Din rail. Not sure if it fits a Wylex busbar, or any busbar.

"Can be fitted on DIN rail directly into the consumer unit."
 
@brianmoooore I agree in this case, and must have missed the previous thread on this.
Out of interest, would your comment mean that 314.4 can never actually be broken if combining radial circuits?
I always follow this, it is two final circuits therefore separate circuit protection.
 
Status
Not open for further replies.

Reply to two radials into an RCBO in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
644

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
720

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top