Morning everyone . Question regarding wiring of new circuits into plastic cu . I’m wiring an extension on a property soon . The consumer unit is under the stairs and it’s plastic it’s all rcbo Wylex board in good condition with a few spare ways . Probably the last of its generation before we moved into metal boards . My question is can I add 3 new circuits and surge protection to the board and still comply with regs . I cant find a definet answer in the regs book . Wondering if anyone else has had this scenario .

Thanks
 
Morning everyone . Question regarding wiring of new circuits into plastic cu . I’m wiring an extension on a property soon . The consumer unit is under the stairs and it’s plastic it’s all rcbo Wylex board in good condition with a few spare ways . Probably the last of its generation before we moved into metal boards . My question is can I add 3 new circuits and surge protection to the board and still comply with regs . I cant find a definet answer in the regs book . Wondering if anyone else has had this scenario .

Thanks

If the CU is is good condition with no signs of thermal damage then I would just make a note on the Installation Certificate that you have advised the client about the change regarding Plastic Consumer units since it is located under the stairs. I would do this on Comments on Existing Installation.

I would do this just to cover yourself.

As competent persons if we see anything that may require attention we are supposed to report it to the duty holder.
 
My question is can I add 3 new circuits and surge protection to the board and still comply with regs .
How are you planning to go about the certification and notification process? Are you a member of one of the CPS scams?
 
If the CU is is good condition with no signs of thermal damage then I would just make a note on the Installation Certificate that you have advised the client about the change regarding Plastic Consumer units since it is located under the stairs. I would do this on Comments on Existing Installation.

I would do this just to cover yourself.

As competent persons if we see anything that may require attention we are supposed to report it to the duty holder.
Thanks . I was thinking similar to what you’ve said 👍
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Whitehaven
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
If other, please explain
Installation electrician

Thread Information

Title
New circuits into plastic consumer unit
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
Km1777,
Last reply from
Km1777,
Replies
4
Views
784

Advert

TrueNAS JBOD Storage Server

Back
Top