I need advice on whether or not I can use the original wires that bring power into my detached structure.
The photos show the exterior connection from the power lines that would have a dial from the power company when active. It's currently not active. Another photo shows the exterior wiring running along the wall and entering the structure. Another photo shows the old breaker box that I want to replace with a modern one and the wires coming into it from the outside. There is a ground wire. I'm not sure what the wire gauge is. The old wiring does have a rubbery kind of insulation wrapped in cloth. It seems to be pretty well intact.

Question: Is it legal for me to keep the wiring up to the breaker if I connected it to a new breaker box? Also. Any advice on determining the gauge of wire. It is copper, and I see 7 strands. Each strand is 1/16” exactly measured with my calipers.

Thanks in advance for any advice!
 

Attachments

  • [ElectriciansForums.net] I need advice on rewiring my workshop.
    PXL_20210710_183400755.jpg
    657 KB · Views: 46
  • [ElectriciansForums.net] I need advice on rewiring my workshop.
    PXL_20210710_183417840.jpg
    549.1 KB · Views: 39
  • [ElectriciansForums.net] I need advice on rewiring my workshop.
    PXL_20210710_183440464.jpg
    504.7 KB · Views: 38
  • [ElectriciansForums.net] I need advice on rewiring my workshop.
    PXL_20210710_183448855.jpg
    399 KB · Views: 39
I need advice on whether or not I can use the original wires that bring power into my detached structure.
The photos show the exterior connection from the power lines that would have a dial from the power company when active. It's currently not active. Another photo shows the exterior wiring running along the wall and entering the structure. Another photo shows the old breaker box that I want to replace with a modern one and the wires coming into it from the outside. There is a ground wire. I'm not sure what the wire gauge is. The old wiring does have a rubbery kind of insulation wrapped in cloth. It seems to be pretty well intact.

Question: Is it legal for me to keep the wiring up to the breaker if I connected it to a new breaker box? Also. Any advice on determining the gauge of wire. It is copper, and I see 7 strands. Each strand is 1/16” exactly measured with my calipers.

Thanks in advance for any advice!
If I was you I would tear out all the old stuff and start from scratch and especially the meter base. The size wire you have right now is 1/0 aluminum wire which in my opinion needs to go. Good luck
 
Even new USA wiring looks like somethin out of the 1950s or 60s to UK eyes, but that really does look to be well past it's use by date.
more like 1930's, judging by the OP's pics.
 
Only a fool would even think of using any part of that wiring ! .Remove every single bit .Plan a new set up and go from there .
 
I agree with others here, replace it as going to have to get a permit to reestablish power anyway, and the equipment was past it's prime 60 years ago. I doubt it would be allowed to be reconnected without new equipment.
 

Reply to I need advice on rewiring my workshop. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
There is nothing inherently wrong with this part of the layout. There is another option that you may want to consider. Those supply conductors...
Replies
3
Views
1K
  • Question
It would be more helpful if you could tell us what the HP is on the motor since it will have to be considered a continuous duty motor since it...
Replies
1
Views
342
  • Question
Interesting item you have there. This blog might be worth a read https://sllipblog.wordpress.com/2014/04/29/its-now-00-28am-and-i-need-my-bed/...
Replies
9
Views
413
  • Question
How did it go?
Replies
12
Views
2K
  • Question
Yes you will need to install # 4 wiring times 4 for your 2 hots, 1 neutral and 1 equipment ground. As for keeping the grounds and neutrals...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks