Hey everyone thanks for reading.

We are having an issue with our cone crusher and starting. We have had engineers design the motor and starter know the full application and torque requirements of the cone crusher.

We are having intermittent starting issues. And have been for 2 years no one has been able to work out what is happening. We are using a soft starter and we change current limit settings. Does not matter if we increase it or then decrease it back to original settings it will then start. It will run and run and start then just not start. We change current limiting start up settings then it will start.

Bit of context on the site. A lot of electricians have been through and we have come to a common theory of it being a power quality issue. The whole site is run on diesel gensets and our power factor correction, due to lightning damage, is limited. We have our smallest filter and largest filter and we have a rectiformer that is always increasing and decreasing its draw and forever chasing the ideal power factor and at times crushing start up is an issue due to the sizes of our only 2 filters left that have to be manually controlled.

We get fitters to remove the guard and can spin freely and have removed belts and always starts up.

Can anyone shed some light on the effects of power quality with motor start up? The soft starter faults out on F4 - current limit start time expired.
 
Have you considered changing it to star - delta starting, it will not be affected much by power quality issues unlike the electronic soft start unit.
 
Have you considered changing it to star - delta starting, it will not be affected much by power quality issues unlike the electronic
No we haven’t. The design has come the electrical and mechanical engineers who are contractors.

I don’t know a lot about star delta starting but I don’t think we’d have the torque requirements for starting it.

I have been on this site for 6 months and always having call outs to this particular motor and now all I did is slightly adjust the current limit on startup and it will then work. Operators think I’m a genius. Next time it won’t start I’ll adjust it back to what the engineer has specified and it works..
 
start-up torque should be about 1/3 of the rated motor torque in delta.
 
Have you talked to the gen' suppliers, certain equipment can massively reduce the gen's full load capability, I look after a stone yard and we lose 30%-40% of the generators plated FLC due to large VSD's been on the system, you say its a soft start but functionally the do start a motor up in a similar fashion so could be putting limitations on the generator.
 
Have you talked to the gen' suppliers, certain equipment can massively reduce the gen's full load capability, I look after a stone yard and we lose 30%-40% of the generators plated FLC due to large VSD's been on the system, you say its a soft start but functionally the do start a motor up in a similar fashion so could be putting limitations on the generator.
Yeah when we start up the cone crusher the power factor can drop from .9 to .5. I’ve seen it drop down to .4 during start up. We have more than enough spinning reserve to supply the start up load but the power factor drops so much you can see the lights dim/flicker shortly.

reactive power would increase so much which would then decrease the FLC of the generators. We have about 1.5Mw spinning reserve. It has knocked the site out before but usually when our PF is low for start up.

It makes us all think about the effect of reactive power of the motor on startup when the PF can drop so low.

we can’t get instantaneous readings during startup with the system we have there is a bit of a delay. We are thinking of installing a data logger on the cone crusher so we can see it when it doesn’t startup verse when it starts and go from there.
 

Reply to 375kw squirrel cage 415v motor starting issues in the Electrical Engineering Chat area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
698
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
790
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

Hello, Last year my 30 year old Static Pase convertor stopped working, the 3 phase motor is 0.55KW / 0.74HP and drives a small lathe. When I...
Replies
0
Views
288
I challenged a council on having the same system installed in an HMO. One consideration is if the flats/escape route were made to The Building...
Replies
1
Views
396

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top