RobTheBob

DIY
Joined
Aug 15, 2021
Messages
3
Reaction score
0
Location
Norwich
Replacing my hob and found this. Hob (6.4kW) installed on a dedicated 32A circuit, wired with 6mm TE. Five terminals on the hob, two lives and two neutrals have each been bridged with 1.5mm wire. TE cable is wired to one of the lives and one of the neutrals. Is this correct? Thank you
 
the bridging links are usually flat brass links, fitted by manufacturer. should not be wire. check manual for wiring diagram/s. your fixed wiring supply is correct.

as always. a photo would help.
 
Thank you telectrix for your reply.

Weirdly my new hob didn't come with the brass links
Hopefully you can see the image attached

The hob as new is supplied with 5 core 1.5mm cable

Thank you again.
 

Attachments

  • [ElectriciansForums.net] Hob wiring question
    IMG20210814165426.jpg
    309.5 KB · Views: 69
Put the flex back on it, the crimp lugs have not been terminated properly, looks like plier marks not crimp indentations

the cable is not heat resistant, it probably should be but a check in the manual should confirm.
 
I would rather rely on factory crimps on the 5 core 1.5mm flex originally supplied by the manufacturer (with one tag on each terminal, and then appropriately joined remotely), than DIY crimps on 6mm solid conductor cable.

The links in the photo seem to have a factory crimp one end, and a DIY crimp the other, showing the same sort of marks that James mentions above. Could they be made from the flex?

It's most important to use a good quality ratchet crimp tool to make such joints, especially on solid conductors.
 
Agree with everything above.
if the power was turned off and the cable tugged a little, I would bet the cable comes out of the crimp with ease.
 
Probably a quick job for a sparky with the correct tools and parts in the van.

I would not suggest a DIY repair on this.
 
As above, the crimps on the 6mm twin and earth are dangerous and should be removed. Someone has also used the incorrect crimp for the 2.5mm cpc, it should be blue.
A good quality ratchet crimper needs to be used otherwise the joints will heat up and eventually fail. Worst case scenario is a fire.
 
As above, unsiatisfactory crrimping with unsuitable tools and connectors that will likely result in overheating, maybe not now while the copper is clean and bright but in a year or two once it has oxidised. A properly made crimp needs not only to be mechanically attached, but to make a gas-tight cold-weld between cable and terminal.
 
Look inside the terminal block of your new Hob, you may find the brass links already there, but as others have said, should really be heat proof flex, especially if the hob is above an oven with a cover plate between the two with reflective foil.
 
Is the photo your new hob or old one?

the new one should have all the bits needed, including a length of appropriate flex, with crimped ends, and any copper links. (Check they’re not in a bag with fixing brackets)

If in doubt, RTFM
 
Thank you all very much for your replies.

So other than the poor crimping on the ferrules, and the lack of heat resistance, the actual wiring is correct?

Thank you again,
There are no other parts of the actual wiring.

what you should have is a switch above the worktop to turn it on and off.
an appliance outlet at the back of the cupboard space to wire the flex from the hob to.
a suitable specified flex (NOT TWIN AND EARTH) between the wall and the hob
correct termination of all conductors and good quality workmanship throughout.

From what you have shown us, ABSOLUTELY NONE OF THAT HAS BEEN ACHIEVED.
 
That 5 core flex needs to go back on and any linking done at the end of the flex not attached to the hob. The 6.0mm cable will be putting enormous strain on those PCB terminals.
 

Reply to Hob wiring question in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
I actually did it with a 4 core 4.0mm swa last week!
Replies
12
Views
735
Hi there , I wired it up following the instructions from similar model. Works great thanks for your help
Replies
4
Views
327

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top