Got called to "a flat in Manchester has no hot water" at 16:30 today and to be frank I was a little miffed to have to attend.

So arrives at site, spends 20mins finding parking, 30 mins finding the site contact, getting keys and then being informed that it was not one flat but eleven.

Have no idea what the supply is, big I'd guess, nor did I have access to ant distribution equipment, just a list of flat numbers.

So I go to the first one. The 16A MCB was off and was informed that "it goes bang if you try to turn it back on" which I took his word for.

So I worked back from the tank, element OK, thermostat OK, wiring OK however the timer was visibly burnt out.

Did a random sample of the other ten and of the four I checked out all had the same burnt out timer.

Due to the time nothing more was done and an assumption (I know?) made that all had blown.

The only other thing I did was to check the local voltages and all were 236-7V and steady, for the brief time I observed.

These flats were all over, not just one floor so unlikely to be from a single phase or distribution board.

The tennants all made the same complaints of flickering lights and one long recent power outage.

None of the staff had any knowledge.

----es me off that there is nobody on site with any ownership, or understanding of the buildings and their systems, there are two blocks approx 400 flats for christ sake.

I'm half tempted to just replace the controllers and note there may be underlying issues that need further investigations.

How would you guys approach this?
 
My thinking of what we have so far.

The catastrophic failure or the MOV (thanks) in the controller would point to a large over voltage situation.

It is most probably not environmental but a lost Neutral.

Without further information this could be anywhere internal or external.

So I was thinking to approach it on two fronts, to contact the DNO and report a possible Neutral fault whilst surveying the site, reported faults and drawings to see if a pattern can pinpoint the location.

So in a normal fault free situation the installation should look like.
[ElectriciansForums.net] Block of 200+ flats, eleven single channel hot water timers blown this week alone.


If the fault is in the below position then I should only be hearing of power outages in flats 7, 8 & 9 but not over voltages or the MOV failures I'm seeing.
[ElectriciansForums.net] Block of 200+ flats, eleven single channel hot water timers blown this week alone.


If the fault is in the below position then flats 4, 5 & 6 and flats 7, 8 & 9 will see voltage fluctuations between 0V and 400V depending on their respective loads, this situation could cause the MOV failures.
[ElectriciansForums.net] Block of 200+ flats, eleven single channel hot water timers blown this week alone.


And finally, in the below image the fault would be evident across all phases and all flats with under and over voltages. Whilst there are sections of the internal installation that could contain the fault; in this scenario the fault could also be external.
[ElectriciansForums.net] Block of 200+ flats, eleven single channel hot water timers blown this week alone.


Ii actuality I have already informed the client of the liklihood of a serious fault existing and that it may be internal or external and they will be picking it up from here.

I'm quite disappointed really as its quite interesting to see how far you can fault find on paper if you have enough information.
 

Attachments

  • [ElectriciansForums.net] Block of 200+ flats, eleven single channel hot water timers blown this week alone.
    20210821_084130.jpg
    208.2 KB · Views: 25
Your explanation of the possible scenarios is correct but the configuration in pic.3 is unlikely to exist in practice. Each single phase service will be derived from a 3-phase busbar, with neutrals normally serving one or three phases but seldom two.

If the fault was a cable strike, the neutral may have not merely been broken but also shorted or arced over to a line. A variety of different voltages may have been impressed on the loads in quick succession as the fault developed.
 
I don’t think the burned out disc is an MOV. The timer uses a transformer less way of producing low voltage dc to operate the electronics. I reckon one can see a bridge rectifier - the white block component, and a disc capacitor in series with a resistor of suitable power rating together forming a mains to low voltage dropper. The placement of the resistor and the disc capacitor makes me think their right hand ends are connected to Lin and Nin respectively and their left hand ends to the ac inputs of the bridge rectifier which are normally the inner two leads for this style of rectifier. There is a smoothing capacitor to the left of the bridge rectifier. I reckon the gold rimmed cylindrical component above the relay is a battery for keep alive in the event of power cut and accumulator to handle short duration current surges when the relay turns on.
 
Last edited:
I don’t think the burned out disc is an MOV. The timer uses a transformer less way of producing low voltage dc to operate the electronics. I reckon one can see a bridge rectifier - the white block component, and a disc capacitor in series with a resistor of suitable power rating together forming a mains to low voltage dropper. The placement of the resistor and the disc capacitor makes me think their right hand ends are connected to Lin and Nin respectively and their left hand ends to the ac inputs of the bridge rectifier which are normally the inner two leads for this style of rectifier. There is a smoothing capacitor to the left of the bridge rectifier. I reckon the gold rimmed cylindrical component above the relay is a battery for keep alive in the event of power cut and accumulator to handle short duration current surges when the relay turns on.
A picture of the underside of the PCB would be handy.
 
The white block will be the dropper capacitor, the bridge rec will be SMD. But yes, let's see some pics of the PCB
 
Don't think it's been asked, but did all eleven flats loose their timers at the same time, or was it cumulative over a period.
Following MJ’s theme - MOVs do degrade each time they react to over voltages. It is not unknown for them to eventually suffer thermal runaway which is when their quiescent current rises over time, the MOV warms up, its resistance reduces, it passes more current, it warms up even more…until it cannot dissipate the heat quickly enough to its surroundings and it destructs. All of which can happen in the absence of any overvoltage.
 
Don't think it's been asked, but did all eleven flats loose their timers at the same time, or was it cumulative over a period.
That is a good question but impossible to get a definitive answer as we don't know when they "went" only when the tenant discovered and reported them.

The first was reported on Tuesday, I was called on Thursday and by then there were eleven.

All we've got is the times they were reported.

But judging by the crazy disco lights I witnessed the issue is still ongoing and more will go.
 
@marconi I'll let you off if you can find a SIL through-hole bridge rec in a white package made in the last 25 years.?

We can now confirm from the PCB pics that the failed part is across the mains input. In theory it could have been a small filter capacitor but:
a) The part shape and burst pattern are more consistent with an MOV
b) A cap of those dimensions would typically be a Y-class part of a few nF which is not appropriate there.
c) An MOV is not a bad idea where a capacitive dropper is tapped off the supply to a relay-switched 16A load of unspecified characteristics.

What it will hopefully have been doing, before it popped, was shaving off transients likely to damage the dielectric of the X2 dropper cap, that would otherwise cause a progressive loss of capacitance to the self-healing process.

But judging by the crazy disco lights I witnessed the issue is still ongoing and more will go.

Somebody needs to switch this lot off now.
 

Reply to Block of 200+ flats, eleven single channel hot water timers blown this week alone. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
181
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
556
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
516

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top