Discuss FIRE RATED DOWNLIGHTS AND PLASTIC CCU - WHAT SIDE OF THE FENCE? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
hahaAs a Napit member, my considered opinion is that the book you mention is only fit for one purpose....
View attachment 89661
Thanks for that, I appreciate you taking the time. I will go and have a look at those Regs.As far as I know BS7671 isn't anywhere near that specific. In a nutshell the luminaire must be suitable for the location.
Have a gander at regs 422.3.1, 422.3.8 and 559.4.1
For purposes of an EICR judgement about whether it's potentially dangerous is mainly down to factors mentioned earlier.
A completely separate question is whether the ceiling needs to be fire resistant (FR), as Tel was saying earlier. If the property is divided into multiple dwellings i.e. flats then the fire rated downlight topic comes into play.
A house rented as a whole doesn't come into this category. (A house of multiple occupation has many extra requirements regarding fire safety but not fire retardant ceilings to the best of my knowledge)
Im not trying to force anything, what would you code the downlights as?
no code unless there's problems like thermal damage, exposed inner insulation, etc.Thank you, how would you code the non fire rated downlights?
Thanks for thatAs others have pointed out, non fire rated downlights are okay in some situations, but not in others. If a downlight is installed in a ceiling that is a fire barrier between 2 fire compartments, then it should be appropriately fire rated.
It's not always obvious if a ceiling is a fire barrier, but there may be clues, eg. ceiling is double plasterboarded, is there a fire door somewhere between the downstairs and upstairs rooms separated by the ceiling, different dwellings and so on.
There is a little bit of info in the Electrician's Guide To The Building Regs (10.2.3, and appendix D in the 17th edition, I need to update). Also, there is an excellent youtube vid by John Ward that you will find very useful:
Thanks, good to get confirmation that there is no regulation that I may be disobeying. When I started reading into it , the literature was more about the fire integrity of the floor/ceiling with little mention of the lights themselves being burning hot little things sat in among all the tinder crap you can often find under floor boards.There seems to be a bit of confusion as to the purpose of installing fire rated downlights.
Some seem to have got hold of the idea that a fire rated downlight is needed to prevent a fire starting within or around a downlight. This is not the case.
The purpose of a fire rated downlight is solely to maintain the integrity of the fire barrier that has been penetrated by the insertion of the said light fitting, in order to prevent the spread of fire between the fire compartment below the ceiling, to another fire compartment above the ceiling.
In a normal domestic property, there is only one fire compartment, ie the whole building, therefore no fire rated downlights will be necessary.
The situation is different in special cases, for instance, as @westward10 mentioned, if it's a listed building, or if the building is an HMO.
Having said all of that, I personally always fit fire rated downlights, because it makes sense to do so. But there is no regulation, electrical or building, that can be cited in order to enforce them in most domestic properties.
1. This does not directly reference whether or not the lights themselves are fire rated. (As has been mentioned by @Pretty Mouth , some open back downlights are fire rated)Just noticed NAPIT code breakers have it as a C2.
They say "no fire hoods fitted on open back downlights with room above" C2
C3 if there is no room above
??????
Reply to FIRE RATED DOWNLIGHTS AND PLASTIC CCU - WHAT SIDE OF THE FENCE? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net