So apart from the respected opinions of electricians,which is appreciated, and the advice given in Napits code breakers(not respected by all), there is no bit of literature that says for definite,it simple terms that non fire rated downlights are or are not permissible when carrying out a condition report.
 
As far as I know BS7671 isn't anywhere near that specific. In a nutshell the luminaire must be suitable for the location.
Have a gander at regs 422.3.1, 422.3.8 and 559.4.1
For purposes of an EICR judgement about whether it's potentially dangerous is mainly down to factors mentioned earlier.

A completely separate question is whether the ceiling needs to be fire resistant (FR), as Tel was saying earlier. If the property is divided into multiple dwellings i.e. flats then the fire rated downlight topic comes into play.
A house rented as a whole doesn't come into this category. (A house of multiple occupation has many extra requirements regarding fire safety but not fire retardant ceilings to the best of my knowledge)
 
As far as I know BS7671 isn't anywhere near that specific. In a nutshell the luminaire must be suitable for the location.
Have a gander at regs 422.3.1, 422.3.8 and 559.4.1
For purposes of an EICR judgement about whether it's potentially dangerous is mainly down to factors mentioned earlier.

A completely separate question is whether the ceiling needs to be fire resistant (FR), as Tel was saying earlier. If the property is divided into multiple dwellings i.e. flats then the fire rated downlight topic comes into play.
A house rented as a whole doesn't come into this category. (A house of multiple occupation has many extra requirements regarding fire safety but not fire retardant ceilings to the best of my knowledge)
Thanks for that, I appreciate you taking the time. I will go and have a look at those Regs.
 
Fire protection in listed buildings is of high priority and although the existing ceilings if original or even sympathetically replaced may offer limited protection there may well be retrofitted fire protection you cannot see above them. It is important to know if these light fittings are compromising the fire protection of this building.
 
As others have pointed out, non fire rated downlights are okay in some situations, but not in others. If a downlight is installed in a ceiling that is a fire barrier between 2 fire compartments, then it should be appropriately fire rated.

It's not always obvious if a ceiling is a fire barrier, but there may be clues, eg. ceiling is double plasterboarded, is there a fire door somewhere between the downstairs and upstairs rooms separated by the ceiling, different dwellings and so on.

There is a little bit of info in the Electrician's Guide To The Building Regs (10.2.3, and appendix D in the 17th edition, I need to update). Also, there is an excellent youtube vid by John Ward that you will find very useful:

 
As others have pointed out, non fire rated downlights are okay in some situations, but not in others. If a downlight is installed in a ceiling that is a fire barrier between 2 fire compartments, then it should be appropriately fire rated.

It's not always obvious if a ceiling is a fire barrier, but there may be clues, eg. ceiling is double plasterboarded, is there a fire door somewhere between the downstairs and upstairs rooms separated by the ceiling, different dwellings and so on.

There is a little bit of info in the Electrician's Guide To The Building Regs (10.2.3, and appendix D in the 17th edition, I need to update). Also, there is an excellent youtube vid by John Ward that you will find very useful:

Thanks for that
 
As others have said, C3 for the plastic CU and no code for the downlighters, but I would make a strong recommendation in the notes that they are changed for fire rated versions. I've come across the odd mouse's nest built over a nice warm downlight, featuring pieces of nice dry paper.
 
It's also worth mentioning that not all fire rated downlights are enclosed, can-type ones. Integral Evofire for example are fire rated, but open backed:
 
There seems to be a bit of confusion as to the purpose of installing fire rated downlights.

Some seem to have got hold of the idea that a fire rated downlight is needed to prevent a fire starting within or around a downlight. This is not the case.

The purpose of a fire rated downlight is solely to maintain the integrity of the fire barrier that has been penetrated by the insertion of the said light fitting, in order to prevent the spread of fire between the fire compartment below the ceiling, to another fire compartment above the ceiling.

In a normal domestic property, there is only one fire compartment, ie the whole building, therefore no fire rated downlights will be necessary.

The situation is different in special cases, for instance, as @westward10 mentioned, if it's a listed building, or if the building is an HMO.

Having said all of that, I personally always fit fire rated downlights, because it makes sense to do so. But there is no regulation, electrical or building, that can be cited in order to enforce them in most domestic properties.
 
There seems to be a bit of confusion as to the purpose of installing fire rated downlights.

Some seem to have got hold of the idea that a fire rated downlight is needed to prevent a fire starting within or around a downlight. This is not the case.

The purpose of a fire rated downlight is solely to maintain the integrity of the fire barrier that has been penetrated by the insertion of the said light fitting, in order to prevent the spread of fire between the fire compartment below the ceiling, to another fire compartment above the ceiling.

In a normal domestic property, there is only one fire compartment, ie the whole building, therefore no fire rated downlights will be necessary.

The situation is different in special cases, for instance, as @westward10 mentioned, if it's a listed building, or if the building is an HMO.

Having said all of that, I personally always fit fire rated downlights, because it makes sense to do so. But there is no regulation, electrical or building, that can be cited in order to enforce them in most domestic properties.
Thanks, good to get confirmation that there is no regulation that I may be disobeying. When I started reading into it , the literature was more about the fire integrity of the floor/ceiling with little mention of the lights themselves being burning hot little things sat in among all the tinder crap you can often find under floor boards.
The codebreaker book must responsible for alot of non fire rated downlights being ripped out, certainly when Ive worked helping out on EICRs this has been the case.
 
Just noticed NAPIT code breakers have it as a C2.
They say "no fire hoods fitted on open back downlights with room above" C2
C3 if there is no room above
??????
1. This does not directly reference whether or not the lights themselves are fire rated. (As has been mentioned by @Pretty Mouth , some open back downlights are fire rated)

2. The bit about "the room above" only applies if the room above constitutes a separate fire compartment, which the book fails to point out.

The problem with the Codebreakers book is that it is only a compilation of opinions, with no real explanations given, and mostly vague references to regulations. It can be useful, but like any such opinions, needs to be taken as advice only, and not rigid rules.

(And yes, I do own a copy and have read it through from cover to cover, making notes of my disagreements and actual errors found)
 

Reply to FIRE RATED DOWNLIGHTS AND PLASTIC CCU - WHAT SIDE OF THE FENCE? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
623
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
780
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

  • Question
This potential client seems to be making progress in terms of being interested in proper chargers and answering my query questions. I have also...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top