RCOCB BS 4293 | on ElectriciansForums

Discuss RCOCB BS 4293 in the UK Electrical Forum area at ElectriciansForums.net

banny07

-
Arms
Joined
Aug 2, 2009
Messages
192
Reaction score
39
Hi Guys.
I went to see a job today where customer wanted to replace front plate of sockets and switches. Switches has no cpc but cpc is present in the cieling roses. As I opened consumer unit the main switch was 80A 2 pole RCOCB bs 4293 which has 100mA rated tripping current and 2000A breaking capacity. My question " Is it acceptable in dwellings". customer doesn't want to upgrade consumer unit. Please advise . Thanks in advance
[ElectriciansForums.net] RCOCB BS 4293
[ElectriciansForums.net] RCOCB BS 4293
 
The switch drops may be contained in steel conduit which may in fact be the CPC. Worth getting the tester out to check. If not, then it may be possible to pull in a separate CPC.
If that is not possible, then replacing plastic switches for metal ones would be introducing a potentially dangerous situation.

The 100 mA main switch RCD does not provide additional protection where it is required, eg for sockets used for equipment outdoors. I would be reluctant to take on any changes at all in this situation.
 
nevertle less, you are modifying alighting circuit, so 30mA rcd protection must be provided.
1. for luminaires in a domestic, and
2. for cables buried in walls <50mm .

3. CYA when the shyte hits the fan. judge.
 
nevertle less, you are modifying alighting circuit, so 30mA rcd protection must be provided.
1. for luminaires in a domestic, and
2. for cables buried in walls <50mm .

3. CYA when the shyte hits the fan. judge.

Its like for like replacements, not modifying the circuit... so BS7671 doesnt usually apply.
Of course, it would be better to upgrade.

changing plastic to plastic is not making the installation "less safe" than it is now. whereas plastic to metal would
 
Its like for like replacements, not modifying the circuit... so BS7671 doesnt usually apply.
Of course, it would be better to upgrade.

changing plastic to plastic is not making the installation "less safe" than it is now. whereas plastic to metal would
as i read OP, customerwants to replacefaceplates.i assume this would be for metal, although not specified in OP.
 
The switch drops may be contained in steel conduit which may in fact be the CPC. Worth getting the tester out to check. If not, then it may be possible to pull in a separate CPC.
If that is not possible, then replacing plastic switches for metal ones would be introducing a potentially dangerous situation.

The 100 mA main switch RCD does not provide additional protection where it is required, eg for sockets used for equipment outdoors. I would be reluctant to take on any changes at all in this situation.
Sorry I forgot to mention it is first floor flat. It is mixed of conduit and pvc trunking . They put coving on top of trunking so its lid is not possible to remove.
 
Plastic to plastic will be ok, as long as you use nylon screws or get the ones with plastic screw covers. (I assume it’s metal back boxes? But looking at the kitchen, I’m not so sure)

I don’t believe there is a distance sockets are away from above the cooker, I just know they can’t be in the space directly above the cooker.
 
Is the pictured RCD main switch acceptable? I believe it should be 30mA in domestic installation not 100mA. What would you suggest in this situation? Thanks.
100mA (more so with some delay = type S), is common in TT systems to have earth fault disconnection on the rod's Ra value without too much risk of nuisance trips. Is it a TT or TN system?

30mA would be better from a shock protection point of view but (a) you won't find a new replacement and (b) even if you did there would likely be issues of it tripping on too much accumulated leakage taking out the lights so potentially more risk than the reduction in shock risk.
 
Plastic to plastic will be ok, as long as you use nylon screws
Realistically it is not worth worrying about.

The regs note that small parts that you can't grab are not really much risk as you would simply pull your fingers away. The real dangers for shocks are (1) things you can grab so the effects of the shock are to be unable to release (say handle of mower outside) and (2) areas with water where even momentary contact is likely to lead to a high shock current so even a fraction of a second might trigger heart fibrillation.
 
If the RCD works, I'd get on with it and get out of there!
If it doesn't, this is one where you could easily open a large can of worms that I'd personally choose to keep shut. It would be a rather challenging CU change if it turns out to be required. (Inset CU and looks like conduit for CPC). It's fairly likely the 100ma RCD is for fault protection of a TT system, or maybe it was TT once and is now PME.
I'd do a Zs@DB (remembering there could be parallel paths). If inconclusive I'd test local incoming earth (disconnected) with main switch off .
If I got higher that TNS numbers back I wouldn't get involved beyond advising in writing to customer that the fault protection of their installation couldn't be confirmed and more work is needed to investigate and rectify.
 

Reply to RCOCB BS 4293 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
1K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
636
  • Question
Absolutely, yes. It was just a bit of a joke, looking at your quoted Z values. edit. Oh, joking too!.....I see your attempted smile didn't work ...
2
Replies
28
Views
6K
  • Question
Anything is possible, not everything makes sense, though. It's more than feasible to design/assemble some custom controls to make A do something...
Replies
1
Views
2K
  • Question
Think all electricians will/have received a belt in their time. Doesn't matter how many time you read something like this, and are told to L-N N-E...
    • Like
    • Informative
    • Thanks
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks