I have reason to doubt that any inspection or testing was done before an EICR was issued. The test results on the EICR are identical to those on an EIC issued a year previously. Is this likely, or would you expect some values to differ slightly?

Many thanks.

[ElectriciansForums.net] EICR test results
 
I would send an email to the company asking if they have sent the wrong certificate in error.
Mention in the email that it seems to be an EXACT COPY of the previous years one.
 
Rcd times are unlikley to be a precise match, infact sometimes they can vary by a ms or 2 from one test to the next test 5 minutes later.
 
There should be a section which shows which test instruments were used, is this identical?

When this is completed, it should include the date of calibration (although frequently omitted by many), again is this the same?
 
There should be a section which shows which test instruments were used, is this identical?

When this is completed, it should include the date of calibration (although frequently omitted by many), again is this the same?
There is no date of calibration included in the test instrument details box in the generic schedule of test results.
 
I'm not saying it's not a good idea. It's a great idea.
I only point it out as the OP was talking about reporting it to the NICEIC on the basis of the calibration date not being recorded on the schedule.
I wasn't implying that it's reportable, just that if the test equipment and certification dates are identical, then it adds credence to the suspicion that it's a direct copy; as over 12mths it ought to have an updated calibration certification
 
I have seen a guy sitting in the kitchen typing in a laptop. No tools, test equipment or even a visual inspection. As it was an EICR he was completing I watched with interest and twenty five minutes later he put his laptop in a bag and left.
 

Reply to EICR test results in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

There is one reason to have an inspection every three years instead of the five. It’s more work and money for them 😁😁
Replies
15
Views
2K
Definitely, although most likely within the accessories. I've often found that once accessories are disconnected the cabling IR is fine. Sometimes...
Replies
19
Views
2K
Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
162
Thanks for the reply littlespark. Yes the works have been carried out. Surely it is fraudulent because basically the document is Not...
Replies
2
Views
556
Here the BPG#4 is useful, it is not a statutory document at all, but it provides good guidance as to what can reasonably considered as C1/C2/C3...
Replies
11
Views
645

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks