I have reason to doubt that any inspection or testing was done before an EICR was issued. The test results on the EICR are identical to those on an EIC issued a year previously. Is this likely, or would you expect some values to differ slightly?

Many thanks.

[ElectriciansForums.net] EICR test results
 
I would send an email to the company asking if they have sent the wrong certificate in error.
Mention in the email that it seems to be an EXACT COPY of the previous years one.
 
Rcd times are unlikley to be a precise match, infact sometimes they can vary by a ms or 2 from one test to the next test 5 minutes later.
 
There should be a section which shows which test instruments were used, is this identical?

When this is completed, it should include the date of calibration (although frequently omitted by many), again is this the same?
 
There should be a section which shows which test instruments were used, is this identical?

When this is completed, it should include the date of calibration (although frequently omitted by many), again is this the same?
There is no date of calibration included in the test instrument details box in the generic schedule of test results.
 
I'm not saying it's not a good idea. It's a great idea.
I only point it out as the OP was talking about reporting it to the NICEIC on the basis of the calibration date not being recorded on the schedule.
I wasn't implying that it's reportable, just that if the test equipment and certification dates are identical, then it adds credence to the suspicion that it's a direct copy; as over 12mths it ought to have an updated calibration certification
 
I have seen a guy sitting in the kitchen typing in a laptop. No tools, test equipment or even a visual inspection. As it was an EICR he was completing I watched with interest and twenty five minutes later he put his laptop in a bag and left.
 

Reply to EICR test results in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
308
I usually put something like this To assess compliance with BS7671 for continued safe operation (5 year periodical inspection)
Replies
8
Views
455

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top