Doing an inspection and came across this.
Feeds are as follows:
Cutout to Meter - 25mm
Meter to connector blocks - 25mm
Connector blocks to CU’s (2 in the house) 16mm.
So far so good as the cutout is 80A not the 100A it’s labelled as.
My query is the 6mm 3 core XPLE that’s going to an outbuilding.
At the outbuilding end is 2 way CU with a 40 RCD switch and a 16a socket & 6a light circuit.
Now I know the RCD will stop the cable ever pulling more than 40A. But as it’s wired into those connectors it has the potential to pull 80a (in theory).
I’ve coded it as a C2 as to me it’s potentially dangerous given there’s no OCPD protecting the cable from the connector until it reaches the RCD in CU in the outbuilding. It’s been there approx 8yrs according to the owner and there are no signs of thermal issues anywhere at either end. But thought I’d garner opinion from the more experienced/knowledgeable folk on here.
What would you code it as? Or would you deem it safe given the RCD at the other end?
Feeds are as follows:
Cutout to Meter - 25mm
Meter to connector blocks - 25mm
Connector blocks to CU’s (2 in the house) 16mm.
So far so good as the cutout is 80A not the 100A it’s labelled as.
My query is the 6mm 3 core XPLE that’s going to an outbuilding.
At the outbuilding end is 2 way CU with a 40 RCD switch and a 16a socket & 6a light circuit.
Now I know the RCD will stop the cable ever pulling more than 40A. But as it’s wired into those connectors it has the potential to pull 80a (in theory).
I’ve coded it as a C2 as to me it’s potentially dangerous given there’s no OCPD protecting the cable from the connector until it reaches the RCD in CU in the outbuilding. It’s been there approx 8yrs according to the owner and there are no signs of thermal issues anywhere at either end. But thought I’d garner opinion from the more experienced/knowledgeable folk on here.
What would you code it as? Or would you deem it safe given the RCD at the other end?