Well the op doesn't say there is no cpc, just it's a class II.

So it's just my guess that it might be a transformerless shaver socket, but it would be limited to 200mA of course, probably OK for a laptop, although should be only for shavers.

Agree, if it is this, there isn't any regulation preventing it's placement (assuming it's outside of 3m from the room containing a bath or shower ?).

Where he chooses to shave is up to him.
So i should change fuse in the FCU to 200 mA from 13 to comply ?
 
Still a little confused.

external rated 2 pin socket fitted outside fed from a ring. It is fused down with a 13A FSU and the feed cable has no earth.

is this correct?

what size are the conductors?

is the 2 pin socket a shaver type socket or….. ?

picture would help. If you can’t get picture from on site a similar picture from internet search would be good.
 
In that case not sure what grounds you’ve stated unsatisfactory.

what is the actual reason stated for the coding? And what code did you give?
I went with a C2 Recommended cable change to 3 core and standard S/O plate. Posted this because I've never seen this setup and it just felt wrong.
 
I went with a C2 Recommended cable change to 3 core and standard S/O plate. Posted this because I've never seen this setup and it just felt wrong.
I get what your recommending, but what is your reason for the coding?

in an EICR observations you don’t put what should be there or what should be done. You put what is wrong At the time of inspection.

examples:
disconnection times not achievable due to……

potential for overload because…….

cable not sufficient current carrying capacity due to……

etc….etc…


What was the actual wording in observations for your C2?
 
I get what your recommending, but what is your reason for the coding?

in an EICR observations you don’t put what should be there or what should be done. You put what is wrong At the time of inspection.

examples:
disconnection times not achievable due to……

potential for overload because…….

cable not sufficient current carrying capacity due to……

etc….etc…


What was the actual wording in observations for your C2?
The C2 was simply recorded as not complying with 411.3.3 "Additional Protection by means of an RCD" The recommendation to the customer was cable and S/O change.
 
So i should change fuse in the FCU to 200 mA from 13 to comply ?
If it is a standard transformerless shaver socket outlet, then it is automatically restricted to 200mA internally, the upstream fuse merely needs to be sufficient to protect the cable.

If it is not a transformer or tranformerless shaver socket outlet to bs4573 it is not permitted.

The only socket outlets permitted are those detailed in the regs, ie bs1363, 546 etc.

This isn't just the regs that mandate this, it is actually law SI 1768 1994 - plug and socket regulations.

This is freely available on-line , if you do have a 2 pin eu or similar plug, then the adapter must be included, must be to standard/approved, includes a fuse, and cannot be removed without tools or may have proper shutters etc.
 

Reply to Class 2 Spur to outside socket in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
184
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
560
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
516

Similar threads

Luckily when I rejigged the socket to fit the fcu next to it, it meant the original ring wiring reached, i put the socket on the ring and took a...
    • Like
Replies
8
Views
1K
It depends on where that SFU 'sits' in the circuit. If it's there as a courtesy isolator for the fridge socket then potentially yes as it could...
Replies
2
Views
953

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top