Just completed an EICR which had an Unsatisfactory Report done earlier in the year by another Spark, i have a copy of the report and he's put the earthing system down as a TN-S and a ZE of 0.21. However as you can see the main earthing conductor (16mm) doesn't go to what appears to be a DNO MET, I presume it goes to an earth rod hence the Ze reading I got of 28.2 Ohms and a Zdb reading of 16.2 Ohms. All of my ELIT readings are around the 19 Ohm mark though. I did try a Ze from the DNO's block and got 30 odd Ohms so not sure what it's there for? Any Thoughts? I'm unable to lift the tiled floor in the porch to confirm if an earth rod is installed however from previous experience similar age houses in the same are are TT'd.

[ElectriciansForums.net] Curious DNO MET on TT System
[ElectriciansForums.net] Curious DNO MET on TT System
 
Last edited by a moderator:
I can't seem to expand the 2nd picture which is the important one.
Also, just wondering, is there an up front RCD or RCD main switch on the consumer unit? It looks like either a dual RCD / split load board. Some people have been known to get twitchy about single insulated link cables prior to the RCD protection on a TT setup, rightly or wrongly.
 
Not too well up on the UK stuff

So doesn't look like TN anyhow from the pics , dunno why the external fault loop is 30ohm there on the DNO ? MET

As above I suppose , is there upfront RCD on the board ?
 
I can't seem to expand the 2nd picture which is the important one.
Also, just wondering, is there an up front RCD or RCD main switch on the consumer unit? It looks like either a dual RCD / split load board. Some people have been known to get twitchy about single insulated link cables prior to the RCD protection on a TT setup, rightly or wrongly.

The board was set up as a split load board with 2 Non-RCD protected lighting circuits, No Up-Front RCD, I've moved the two lighting circuits to the RCD protected side.

(The abandoned cables are for cooker and shower which are not being utilised and must be coiled or JB'd somewhere. Also the smoke detector circuit which had the CPC cut out of it for some strange reason, battery ones now installed).

The worrying this is the landlord seems to think it was rewired 12ish years ago meaning the two lighting circuits have had no RCD protection on a TT system for that length of time, the PEFC was 9 amps meaning a direct earth fault would take around half an hour to trip.
 

Attachments

  • [ElectriciansForums.net] Curious DNO MET on TT System
    IMG_3955.jpeg
    493.1 KB · Views: 52
I see what you mean. It looks as though it had an effective TNS setup once.
You could take a length of 2nd hand nicely faded 16mm earth, connect it in addition between that block and the CU and then call the DNO reporting a high Ze. You have evidence they supplied an earth once, and evidence it was once effective (the EICR paperwork).
Chances are it will find itself being changed to TNCS before you can say 'earth rod'.
 
So doesn't look like TN anyhow from the pics , dunno why the external fault loop is 30ohm there on the DNO ? MET

As above I suppose , is there upfront RCD on the board
there you go mikegh .
 
I'd call the DNO it's not that uncommon to find what you have found these days because an electrician CBA to call the DNO and thinks it's easier to knock an earth rod in
 
I'd try a Ze from the block below the meter, looks like a TN just never had the earth connected.
I think he did that and that is what he says is giving 30 ohms! (Can't quote top post for some reason.)

I also think the consumer unit as it stands presents an interesting conundrum regarding regs. As far as I can see it wouldn't have complied with 17th or Amendment 3 without an up front RCD due to the single insulated internal links before the RCD input terminals. Strangely it may comply with 18th in that regard as the revised reg regarding internal links specifically applies to metal consumer units. But other factors make it obvious it wasn't installed to 18th. My point being I can't see a moment in time when it was ok to install exactly that setup.
I'm weighing up whether I'd just move the tails to the top of the RCD and dispense with the main switch completely as to my thinking that would have complied once.

As above, I'd be inclined to contact the DNO saying the TNS earthing is giving a Ze of 30 ohms and the house has no visible means of providing a main earth.
 
Last edited:

Reply to Curious DNO MET on TT System in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
671
  • Question
I think I might be tempted to test this theory, if it can be done without causing danger to anyone.
Replies
11
Views
2K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top