Just completed an EICR which had an Unsatisfactory Report done earlier in the year by another Spark, i have a copy of the report and he's put the earthing system down as a TN-S and a ZE of 0.21. However as you can see the main earthing conductor (16mm) doesn't go to what appears to be a DNO MET, I presume it goes to an earth rod hence the Ze reading I got of 28.2 Ohms and a Zdb reading of 16.2 Ohms. All of my ELIT readings are around the 19 Ohm mark though. I did try a Ze from the DNO's block and got 30 odd Ohms so not sure what it's there for? Any Thoughts? I'm unable to lift the tiled floor in the porch to confirm if an earth rod is installed however from previous experience similar age houses in the same are are TT'd.