What you reckon doing a Eicr loads of these DB’s
 

Attachments

  • [ElectriciansForums.net] 3p Tpn converted to Sp
    7510B4BA-5ACE-4C77-AC03-229469BA1B3C.jpeg
    590 KB · Views: 59
Last edited:
In this case both the L & N of the supply are carrying all of the load, so design-wise it should have upstream OCPD that is rated for that cable (as I suspect the sum of downstream MCBs is way higher).
 
It may have DP isolation but not at that location.
 
The neutral will only require switchable isolation in say a dwelling. Commercially the neutral requires a link to disconnect it
 
For that board no it just links the three lines. I believe the new Eaton ones become a double pole switch which also switches the neutral.
I know that I would fit a DP main switch, never seen a single phase supply without one.
Its a EICR so it’s been in place for some time, classification code C3 maybe after reading all these messages ?
 

Reply to 3p Tpn converted to Sp in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Wasn't paying attention thought it was items of 3P machinery that was being isolated
Replies
8
Views
506
All I know is it is hard to do up gland nuts on the inside top and bottom, side ok
Replies
4
Views
520
  • Question
Not sure if I’ve understood this properly, but it appears to have parallels with my own installation. I highly dislike the idea of feeding SP...
2
Replies
49
Views
5K
N
  • Question
In my first sparking era (late 90's) I was always told to run a neutral to the isolator, as the chances are whoever is using the machine will...
    • Like
Replies
21
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks