[ElectriciansForums.net] Danson Consumer Unit[ElectriciansForums.net] Danson Consumer Unit
When carrying out an EICR I found this board. The live bus bar cuts across the neutral where the tails have exposed copper. Is this the way these boards come? I have never came across this before
Cheers
I would guess (hope!) that it's been assembled incorrectly. The RCD should only serve MCBs to the right of it, so there would be a break in the busbar where the neutral is.
Or do you have both RCDs connected in parallel??
Looks as though it's been assembled with the RCD's on the wrong side of the bus
Thanks for your replys. Yea it seems they have just completely made a mess. The whole job is a shambles. They have 2.5 radials on 32a mcb's no grommets or glands and a lot of other issues. I just count get my head round that bus bar.
Reply to Danson Consumer Unit in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net
I saw some videos talking about RCD's and RCBO's which is what got me curious and to realise how outdated our CU is. I think going forward I'm...
This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1